Great to know. Example files with Chiller upstream or downstream of Ice Storage have both chiller and ice storage in one branch. That is why node names have to match. (i.e. chiller outlet should match ice storage inlet when chiller is upstream and opposite when chiller is downstream) In your input file, Ice storage is placed in the inlet branch in series with the pump. Chiller is then placed in the splitter outlet branch. Splitter also has a bypass branch so you can not specify chiller inlet node name as same as ice storage outlet node name. Ice storage outlet node is splitter inlet node and not chiller inlet node. That is why I just changed chiller inlet node and file ran with your configuration. Hope this helps. Have a great weekend. On 8/10/2012 5:46 PM, Jeremiah Crossett
wrote:
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.