|
Good point (about unmet loads). What does “indirectly conditioned” mean? If there is some type of zone air conditioning, you will not have unmet loads. Thinking about other modeling strategies: · How about specifying a DX or heat pump system with COP = 10,000 and Delta pressure rise = 0? (E+ will accept these values; I have used them.) Approximately zero energy will result, but you will sacrifice correct heat transfer through walls which adjoin conditioned zones. · What if you specify a specific airflow rate in Sizing:System and also make the coils unavailable during normal operations? (I think sizing and operation are calculated separately.) · Let the unmet loads occur, report the hours which occur in the unconditioned zones, deduct those from the total and let the GBCI people know what you did in a narrative which explains it. · If those don’t work, you could model the zones with heating and cooling, report the energy using a Meter:Custom and deduct that energy from t
Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |