Re: [EnergyPlus_Support] AirLoopHVAC has no air flow workaround?





Hello James,

All the zones connected to this air loop have no loads. They are all indirectly conditioned.
I think that if I use normal setpoints with always off availability, it will result in hours with unmet setpoints.

On 6.12.2012 01:39, Jim Dirkes wrote:
 

Miroslav,

I’m guessing that this is the only air loop…  I have modeled other buildings where one or another zone had zero load, but always at least one zone had load – with no fatal errors.

How about using normal setpoints and making the availability always OFF?

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Miroslav Bratanov
Sent: Wednesday, December 05, 2012 5:15 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] AirLoopHVAC has no air flow workaround?

 

 

James,
The program stops before the actual simulation. This is the full message from the .err file.

   ** Severe  ** AirLoopHVAC AHU-RHT_BL has no air flow
   **   ~~~   ** Check flow rate inputs for components in this air loop and,
   **   ~~~   ** if autosized, check Sizing:Zone and Sizing:System objects and related inputs.
   **  Fatal  ** Previous condition causes termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=1
   ..... Last severe error=AirLoopHVAC AHU-RHT_BL has no air flow
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.

On 6.12.2012 00:04, Jim Dirkes wrote:

 

Ignore the “error”. It does not prevent the simulation from running and, as you said, indicates a correct and proper condition.

E+ is just letting you know about an unusual condition.

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Miroslav Bratanov
Sent: Wednesday, December 05, 2012 4:46 PM
To: EnergyPlus Support
Subject: [EnergyPlus_Support] AirLoopHVAC has no air flow workaround?

 

 

Hello all,

I have a building with some indirectly conditioned spaces and I am
modeling a system (PVAV with reheat) just to satisfy the requirement of
Appendix G that all conditioned spaces should be simulated as both
heated and cooled. I set higher and lower setpoint temperatures for the
heating and cooling respectfully, so the system would never turn on. But
during the simulation I get a severe error which says that AirLoopHVAC
has no air flow. Of course this is absolutely correct since there are no
any loads.
I wonder if anyone has had such case and what's the way to deal with
this problem?

Any help is highly appreciated!

Thank you!
Miroslav

 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___