Hey Jim,
I think you are right.
0.3 x CFM = W
0.3 x (L/S) /0.472 = W
thus
0.636 x L/S = W
Thanks, Marcin
Marcin Polak, LEED AP BD+C
Energy Engineer Viridian Energy & Environmental A Vidaris Company T: 212.689.5389 x213 mpolak@xxxxxxxxxxxxxx www.vidaris.com www.viridianee.com From: Jim Dirkes [jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx]
Sent: Friday, April 26, 2013 1:54 PM To: EnergyPlus_Support@xxxxxxxxxxxxxxx; bldg-sim@xxxxxxxxxxxxxxxxxxxxx Subject: Re: [Bldg-sim] Apparent error on ASHRAE 90.1-2007 (and perhaps 2010) Forgot to say: A factor of .636 seems to work better. (SI): (1 L/s * 1000) * .636 = 636 W (This is 1 m3/s) (IP): 2118.64 cfm * .3 = 636 W (This is also 1 m3/s)
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Jim Dirkes
Fabiano, It?s encouraging that they noticed something, however I don?t think the math works properly with the formula you sent. (SI): (1 L/s * 1000) * .14 = 140 W (This is 1 m3/s) (IP): 2118.64 cfm * .3 = 636 W (This is also 1 m3/s)
James V Dirkes II, PE, BEMP, LEED AP
From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Fabiano Domingues Ferreira
Hi Jim,
I was checking 90.1-2010 ? User?s Manual and seems that they have fixed this mistake, follow bellow.
Thanks,
Fabiano Ferreira
De:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Em nome de Jim Dirkes
Dear forums, I think I have discovered an error in the SI version of ASHRAE 90.1 regarding fan power for Baseline Systems 1 & 2. I sent the message below to ASHRAE, but then thought, ?Perhaps someone else has also noticed this and received some guidance from ASHRAE?. Regardless, if it is actually an error, it?s worth mentioning to all of you so that you can be aware of it. Please let me know if you are aware of this, and how you have dealt with the discrepancy. My plan is to use the IP formula because it allows more fan power J.
James V Dirkes II, PE, BEMP, LEED AP
From: Jim Dirkes
Dear ASHRAE, I am comparing Appendix G fan power calculations for ASHRAE 90.1 in both SI and IP units. It appears that they do not agree for Baseline Systems 1 & 2. The formulae for Systems 1 & 2 are: (IP): Pfan (watts) = CFMs (cfm) * 0.3 (SI): Pfan (watts) = CFMs (L/s) * 0.3
Calculating fan power for Systems 1&2: Given: L/s * 1000 = m3/s m3/s * 2118.64 = cfm
Substituting these into the fan power equations for Baseline Systems 1 & 2: (SI): (1 L/s * 1000) * .3 = 300 W (IP): 2118.64 cfm * .3 = 636 W
The fan power should be identical, but isn?t even close! Have you ever noticed this? I could not find an errata sheet that corrected the formula. Will you please check to see if there is a correction? Please make a correction if I am not missing something! Thank you!
p.s., In a smaller way, the fan power calculations do not agree for the other System types. This appears to be due in part to using 5 digit precision for IP units and 4 digits for SI (e.g., 0.00094 for IP and 0.0015 for SI) If you use SI factors of 0.0014857 and 0.0020547 for Systems 3-4 and 5-8 respectively, the agreement is better.
James V Dirkes II, PE, BEMP, LEED AP
The information contained in this communication is confidential, may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any information contained within this communication. If you have received this communication in error please contact the sender by telephone or by response via mail. We have taken precautions to minimize the risk of transmitting software viruses, but we advise you to carry out your own virus checks on any attachment to this message. We cannot accept liability for any loss or damage caused by software viruses. __._,_.___ Primary EnergyPlus support is found at: MARKETPLACE
Switch to: Text-Only, Daily Digest ? Unsubscribe ? Terms of Use ? Send us Feedback . __,_._,___ This e-mail may contain confidential, copyright or privileged information. If you are not the intended recipient or if you have received this e-mail in error, please notify the sender immediately and destroy this e-mail. Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden. |