[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Zone Loads
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Zone Loads
- From: "aleagerman22" <agerman@xxxxxxxxxxxxxxx>
- Date: Thu, 18 Jul 2013 20:43:59 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Thu, 18 Jul 2013 14:44:09 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1374180243; bh=ATjkUZJafyblKp+gzeywgm+C03h1aNbLLyALnUMPacg=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=h2tOk3wldxPDNo8roEtKpdXuVsr4BO4STcT+nOzt3T4WOen00emqUfs5emQ1IarDfO0iP1a6rUv6VwAdCyrKXhjpBIiQYP4pPu9mH2YeWsvFfsjWxMVPYZ3IA0R2jZdpbRRpyNJdPskVm9I3JhqZRszJdxU1JGiiYXT5afKZw7E=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=krmbyYlhrUtLxxVXKFg0YW0zSGycxJDZDori2Qq+xHTdptlkwxRryNztTFMKrZKGlSE0SKyxFjJPxePMvIQlCQ8nbpPLjDGUQ2RRzNMPTb0hWeskiiOwS5TEDNqVClFaGSmgMi4lUNrKt/RcLb9Jhbt3c+q4bKdWknPq1R1KJfA=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <CAPbEBwONfPbBm02xMiAtV=TPwepR+VvWPjr0yHodFJrvm4K2vA@mail.gmail.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Good question, and unfortunately, they don't. I'm missing something on the loads side, the sum of all the variables that I listed previously does not come out to be a reasonable value (it's very low). I will investigate further and provide an update.
For more my purposes I'm thinking of using the delivered energy to the space since my system is able to meet the load in all instances.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Maathangi Sankar <maasankar@...> wrote:
>
> Hi,
> just a quick question, does the sum of all these variables individually
> output match the system output at steady state conditions when the
> temperature set points are met?
>
> I am on the same boat as you too on this issue, if we were to extract the
> same information for a purchased air simulation without including a HVAC
> system, then using zone HVAC doesn't make sense right? You got any ideas
> for that?
>
> sorry I did not have any answers, but just more questions along the same
> lines!
>
> thanks!
>
>
>
>
> On Jul 18, 2013 5:19 AM, "aleagerman22" <agerman@...> wrote:
>
> > **
> >
> >
> > I'm trying to export hourly calculated zone loads from my single zone
> > residential model. I don't see a single output:variable that provides this.
> > I'm using the ZoneHVAC:LowTemperatureRadiant:VariableFlow object for
> > heating and cooling delivery, so it isn't an air delivery system. From what
> > I can gather, for this specific case to obtain the total zone load I need
> > to output individually and sum all of the following. Am I missing
> > something? Thanks for the help.
> >
> > Zone Total Internal Total Heating Rate, !- Variable Name
> > Zone Total Internal Total Heating Energy, !- Variable Name
> > Zone Windows Total Heat Gain Energy, !- Variable Name
> > Zone Windows Total Heat Loss Energy, !- Variable Name
> > Zone Infiltration Total Heat Gain Energy, !- Variable Name
> > Zone Infiltration Total Heat Loss Energy, !- Variable Name
> > Zone Opaque Surface Inside Faces Total Conduction Heat Gain Energy, Zone
> > Opaque Surface Inside Faces Total Conduction Heat Loss Energy, Zone
> > Ventilation Total Heat Gain Energy, !- Variable Name
> > Zone Ventilation Total Heat Loss Energy, !- Variable Name
> >
> >
> >
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/