RE: [EnergyPlus_Support] Low temperature radiant system - check return water temperature?





Just to add to what Jean says, you can generate HVAC node temperature outputs in DesignBuilder by checking the "HVAC System temperatures" option under Miscellaneous Outputs on the Output tab of Simulation options dialog. I think you may need to use v3.3 beta test versions to access this.

 

You can view the return water temperatures in DesignBuilder using the Results Viewer. Instructions for use can be found at:

 

http://www.designbuilder.co.uk/helpv3.3/#ResultsProcessor.htm

 

HW Loop Demand side outlet temperatures will give you the return hot water loop temperatures.

 

Andy

 

Andy Tindale

DesignBuilder Software Ltd

www.designbuilder.com

Tel: +44 (0)1453 755500

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@xxxxxxxxx
Sent: 10 October 2013 20:05
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Low temperature radiant system - check return water temperature?

 

 

0) Search the forum for rdd file. 

 

Re: DesignBuilder

1) Best ask the DB forum...

2) I think the latest versions running e+ v8.0 should include a maximum circuit length. The active area gets used to automatically calculate the number of circuits.

3) there is also a Alpha results viewer from DB

4) you can save extra output variable declarations in a text file with a idf extention in your DB e+ folder and use the include idf dialogue in DB to include this file's text.

Mit freundlichen Grüßen- Sent from my iPhone (excuse the brevity)

 

i. A.

Jean Marais

b.i.g. bechtold

Tel.   +49 30 6706662-23


On 10.10.2013, at 18:01, Athinodoros Tzoulis <a_tzoulis@xxxxxxxxx> wrote:

 

Hello,

 

I am modelling a small room with a heated floor and I would like to check the return water temperature of the system in every step. 

Is there a possibility to apply a sensor or node at the end of the circuit and check water temperatures?

 

Moreover, if the heated floor is concrete core activation the most common way to actually build the system is to have prefab slabs of 1.2m wide and the supply water is coming in from the one side and getting out from the other. So, in this case we have several loops in a room/zone which altogether added are the circuit length. Is there a way to distinguish these two cases (having different circuit length and different loop length)?

 

I am using DesignBuilder initially and then I import the results in EnergyPlus in order to make small changes in EP. So, if you know a way to do it in Designbuilder you are welcome to do so.

 

Thank you very much in advance

 

Best regards,

Athinodoros Tzoulis



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00171.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00221.jpg