Yes, new E+ documentation showing ground source heat pump G-functions has problem of matching figures and comments. Seems some comment fields (lines) are missing so that all the comment fields below those missed texts were shifted up.

Sean 



---In energyplus_support@xxxxxxxxxxxxxxx, <silvia1-@...> wrote:

OK I will try...thank you very much! 



---In energyplus_support@xxxxxxxxxxxxxxx, <leeed2001@...> wrote:

I'm not sure why it didn't work immediately, but the errors are pretty clear:

** Severe  ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.

   **   ~~~   ** ...Pipe Thickness=[998.200].

   **   ~~~   ** ...Pipe Out Diameter=[0.389].

   **   ~~~   ** ...Radius will be <=0.

   ** Warning ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.

   **   ~~~   ** ...Maximum Length of Simulation less than RunPeriod Request

   **   ~~~   ** Requested input=0 will be set to 1


Just go through all the inputs for that object and make sure the values make sense to match that version of E+.  It looks like a field is missing or something.  Because it shows thickness at 998.2, which is more like a density value.



On Fri, Nov 1, 2013 at 10:57 AM, <silvia1-@...> wrote:
 

I've already tried to use one of the dataset g-functions but they gave me some problems...




Program Version,EnergyPlus-Windows-OMP-64 7.2.0.006, YMD=2013.11.01 17:55,IDD_Version 7.2.0.006

   ************* Beginning Zone Sizing Calculations

   ** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.

   **   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.

   ** Warning ** CheckUsedConstructions: There are 4 nominally unused constructions in input.

   **   ~~~   ** Each Unused construction is shown.

   ************* Construction=CONSTGLZ7580

   ************* Construction=CONSTGLZ5679

   ************* Construction=CONSTGLZ4471

   ************* Construction=CONSTGLZ3045

   ************* Beginning Plant Sizing Calculations

   ** Severe  ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.

   **   ~~~   ** ...Pipe Thickness=[998.200].

   **   ~~~   ** ...Pipe Out Diameter=[0.389].

   **   ~~~   ** ...Radius will be <=0.

   ** Warning ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.

   **   ~~~   ** ...Maximum Length of Simulation less than RunPeriod Request

   **   ~~~   ** Requested input=0 will be set to 1

   **  Fatal  ** Errors found in processing input for GroundHeatExchanger:Vertical

   ...Summary of Errors that led to program termination:

   ..... Reference severe error count=1

   ..... Last severe error=GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.

   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).

   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.

   *************

   ************* ===== Final Error Summary =====

   ************* The following error categories occurred.  Consider correcting or noting.

   ************* Nominally Unused Constructions

   ************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause

   ************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm

   ************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).

   *************

   ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.

   ************* EnergyPlus Sizing Error Summary. During Sizing: 2 Warning; 0 Severe Errors.

   ************* EnergyPlus Terminated--Fatal Error Detected. 3 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 10.01sec 



---In energyplus_support@xxxxxxxxxxxxxxx, <leeed2001@...> wrote:

G-functions are not specific to a building, but specific to a borehole (field).  E+ contains a small dataset of g-functions (<E+ install dir>/DataSets/GLHERefData.idf) that you may be able to use that closely meets the needs of your building.  If you need something more specific, you'll have to figure out a way to generate a more specific g-function (http://www.hvac.okstate.edu/research/Documents/ASHRAE/Yavuzturk_Spitler_99.html).


On Fri, Nov 1, 2013 at 10:33 AM, <silvia1-@...> wrote:
 

Hi, I'm a student and I don't have GSHE-Pro but I need a G-function for my research on energy efficiency measures and I want ask if someone can generate for me a G-function specific for my building? Thanks




--
Edwin Lee, PhD
Engineer, Commercial Buildings Research Staff
National Renewable Energy Laboratory




--
Edwin Lee, PhD
Engineer, Commercial Buildings Research Staff
National Renewable Energy Laboratory



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___