RE: [EnergyPlus_Support] Chilled ceiling radiated and convective output





Brent,

 

Thank you.

 

Still, it doesn’t make sense:

 

Chiller electric Power: + 7.4 kW

Surface Inside Face Conduction Heat Transfer Rate = -7.2 kW

Surface Inside Face Conduction Loss Gain Rate = + 7.2 kW

 

Surface Inside Face Convection Heat Gain Rate = + 2.9 kW

Surface Inside Face Net Surface Thermal Radiation Heat Gain Rate= +3 kW

 

I would expect the sum of the convection and the Thermal radiation component to be almost equal to 7.2 kW�.>

 

 

Best regards,

 

Geert

 

 

 

Van: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Namens Griffith, Brent
Verzonden: vrijdag 8 november 2013 20:35
Aan: EnergyPlus_Support@xxxxxxxxxxxxxxx
Onderwerp: RE: [EnergyPlus_Support] Chilled ceiling radiated and convective output

 

 

Hi Gert,

 

I think you miss-understand the directionality.  For most all of the surface outputs, positive values mean the flow of energy is directed toward the *face* of the surface.  If your ceiling is cooling the zone then the conduction will be directed away from the face and into the surface’s construction assembly adjacent to the face.  The “Gain” version of the output variable will be zero but the “Loss” version will be positive. 

 

For thermal radiation, see variables like “Surface Inside Face Net Surface Thermal Radiation Heat Gain Rate”. 

 

You may have turn on display advanced output variables to see all of the options.

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of geert.bellens@xxxxxxxxxxxxxxxxxxxxxx
Sent: Friday, November 08, 2013 4:30 AM
To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Chilled ceiling radiated and convective output

 

 

I'm modelling a chilled ceiling.

 

I have the "Surface Inside Face Conduction Heat transfer Rate " Which gives me an idea of the heat transfer between the zone and the ceiling.

 

If I want to look to the radiant and the convective part, I'm a bit confused about which output to look at.

 

"Surface Inside Face Convection Heat Gain Rate" gives me the convective part, which is about 40 % of the total Heat Transfer Rate.

 

"Surface Inside Face Conduction Heat Gain Rate" is however zero.... which cannot be the case.

 

Am I looking at the wrong output ?

 

 

Geert

 

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___