RE: Re: [EnergyPlus_Support] Loads not met when using HVACTemplate Objects





Thanks for replying back Oscar


I was using a relatively small tolerance for hours not met in OutputControl:ReportingTolerances


Changed to 0.5 deltaT and this flag basically goes away.



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <eng.ohw@...> wrote:

Try to modify the sizing factor. And look carefully the internal walls maybe the conctats are not ok.

Good luck.

Oscar

On Nov 28, 2013 7:42 PM, <sbucking@...> wrote:
 

Hi Everyone,

I am running some batch simulations which swap in/out HVACTemplate objects for various mechanical systems all being auto-sized.

I am noticing that HTMLs indicate that many systems have 100's of hours where heating/cooling loads are not met. I can make some headway by modifying each file directly but the process is very slow. Since I am comparing systems directly, I need to ensure that setpoints are equally for all options.

Does anyone have advice on how I should be approaching this? Can it be solved from the HVACTemplate level (ie without modifying expanded IDFs)?

Many Thanks,

Scott



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___