An “air curtain” in the USA is strictly a fan that recirculates air at a door.  Occasionally it has a heating source.  (For some automotive applications, it is also uses 100% outdoor air!)

·         A recirculating fan cannot change zone air pressure, only the micro-climate pressure in the immediate vicinity of the door. (Consider the definition of 100% recirculation!)

·         The device normally cycles on when the door opens, and may have a minimum operating cycle time, so you will need to determine approximate operating time and reflect it in a schedule.

o   The fans often discharge air at high velocity (20 m/s | 4000 f/min) and are fairly low efficiency, so they use significant power.

·         If they have heating capacity, discharge temperature is often fixed at about 35-40C.  (You should confirm this with the design engineer or temperature controls schematics)

·         It seems impractical to precisely account for mixing between zones, but you might assign a fraction to each of the adjacent zones.  I think I would put all the energy in the “cold” zone (e.g., warehouse)

 

Good luck!  This should not be difficult for you.

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@xxxxxxxxx
Sent: Wednesday, December 11, 2013 2:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Air Curtains Modeling

 

 

If anyone has some experience modelling air curtains in e+, I would also like to know.

 

I would guess the space is over pressurized. Check the AHUs air balances. A percentage of the heat from the unit will be locally lost without "entering" the zone proper (much like a cooker with a hood exhaust).

 

A good place to start is a manufacturer data sheet. Keep us posted.


On 11.12.2013, at 06:11, "hisham.rashrash" <hisham.rashrash@xxxxxxxxx> wrote:

 

Dear all,
I have a warehouse project where hot-water-heated air-curtains are installed over gates for storage spaces and electrically-heated air-curtains are installed over doors for offices.

I am not sure how to model them. Should these be considered as internal loads? then I am not sure of what schedule to follow, also, not sure about the way I should account for mixing of cold air running into zones when gates or doors assumed open and air-curtains are running.

Total power for these air-curtains is 2.5[MW]!!!

Please advise.

Thank you very much.

Hisham



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___