[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Air Curtains Modeling





Interesting discussion. I have to model a building where there are air curtains (aka "air doors") for a LEED project. Would you model them in the same way in the baseline model and in the proposed model? Can it be considered heating energy (it would be strange, because it doesn't work when the internal zone needs heat, but when the door is opened) or process energy?
Do you advice some particular objects of EnergyPlus to model air curtains? 
Regards


---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

Hisham,

An â??air curtainâ?? in the USA is strictly a fan that recirculates air at a door.  Occasionally it has a heating source.  (For some automotive applications, it is also uses 100% outdoor air!)

·         A recirculating fan cannot change zone air pressure, only the micro-climate pressure in the immediate vicinity of the door. (Consider the definition of 100% recirculation!)

·         The device normally cycles on when the door opens, and may have a minimum operating cycle time, so you will need to determine approximate operating time and reflect it in a schedule.

o   The fans often discharge air at high velocity (20 m/s | 4000 f/min) and are fairly low efficiency, so they use significant power.

·         If they have heating capacity, discharge temperature is often fixed at about 35-40C.  (You should confirm this with the design engineer or temperature controls schematics)

·         It seems impractical to precisely account for mixing between zones, but you might assign a fraction to each of the adjacent zones.  I think I would put all the energy in the â??coldâ?? zone (e.g., warehouse)

 

Good luck!  This should not be difficult for you.

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@...
Sent: Wednesday, December 11, 2013 2:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Air Curtains Modeling

 

 

If anyone has some experience modelling air curtains in e+, I would also like to know.

 

I would guess the space is over pressurized. Check the AHUs air balances. A percentage of the heat from the unit will be locally lost without "entering" the zone proper (much like a cooker with a hood exhaust).

 

A good place to start is a manufacturer data sheet. Keep us posted.


On 11.12.2013, at 06:11, "hisham.rashrash" <hisham.rashrash@...> wrote:

 

Dear all,
I have a warehouse project where hot-water-heated air-curtains are installed over gates for storage spaces and electrically-heated air-curtains are installed over doors for offices.

I am not sure how to model them. Should these be considered as internal loads? then I am not sure of what schedule to follow, also, not sure about the way I should account for mixing of cold air running into zones when gates or doors assumed open and air-curtains are running.

Total power for these air-curtains is 2.5[MW]!!!

Please advise.

Thank you very much.

Hisham



__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___