[EnergyPlus_Support] Re: Air Curtains Modeling



Dear James,
Thank you for information provided in your reply, it is appreciated.

Hisham 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Jim Dirkes <jim@...> wrote:
>
> Hisham,
> An â??air curtainâ?? in the USA is strictly a fan that recirculates air at a door.  Occasionally it has a heating source.  (For some automotive applications, it is also uses 100% outdoor air!)
> 
> ·         A recirculating fan cannot change zone air pressure, only the micro-climate pressure in the immediate vicinity of the door. (Consider the definition of 100% recirculation!)
> 
> ·         The device normally cycles on when the door opens, and may have a minimum operating cycle time, so you will need to determine approximate operating time and reflect it in a schedule.
> 
> o   The fans often discharge air at high velocity (20 m/s | 4000 f/min) and are fairly low efficiency, so they use significant power.
> 
> ·         If they have heating capacity, discharge temperature is often fixed at about 35-40C.  (You should confirm this with the design engineer or temperature controls schematics)
> 
> ·         It seems impractical to precisely account for mixing between zones, but you might assign a fraction to each of the adjacent zones.  I think I would put all the energy in the â??coldâ?? zone (e.g., warehouse)
> 
> Good luck!  This should not be difficult for you.
> 
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef@...
> Sent: Wednesday, December 11, 2013 2:26 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Air Curtains Modeling
> 
> 
> If anyone has some experience modelling air curtains in e+, I would also like to know.
> 
> I would guess the space is over pressurized. Check the AHUs air balances. A percentage of the heat from the unit will be locally lost without "entering" the zone proper (much like a cooker with a hood exhaust).
> 
> A good place to start is a manufacturer data sheet. Keep us posted.
> 
> On 11.12.2013, at 06:11, "hisham.rashrash" <hisham.rashrash@...<mailto:hisham.rashrash@...>> wrote:
> 
> 
> Dear all,
> I have a warehouse project where hot-water-heated air-curtains are installed over gates for storage spaces and electrically-heated air-curtains are installed over doors for offices.
> 
> I am not sure how to model them. Should these be considered as internal loads? then I am not sure of what schedule to follow, also, not sure about the way I should account for mixing of cold air running into zones when gates or doors assumed open and air-curtains are running.
> 
> Total power for these air-curtains is 2.5[MW]!!!
> 
> Please advise.
> 
> Thank you very much.
> 
> Hisham
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/