RE: [EnergyPlus_Support] RE: Night cycle Operation




Fabiano,

Availability and setpoint are different concepts.

If the coil is “available” (and the fan is also “available”), the setpoint will be applied. If the coil is not available, the setpoint is not used.

p.s., Yes, there are often different setpoints for a cooling coil and a heating coil, but the setpoints do not need to be different.  A VAV system, for example, might use a constant discharge temperature setpoint of ~12C.



James V Dirkes II, PE, BEMP, LEED AP
<http://www.buildingperformanceteam.com/>www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of fabianoferreira27@xxxxxxxxxxx
Sent: Thursday, February 13, 2014 11:31 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] RE: Night cycle Operation





Hi Jim,



I just need to set the coil availability always “ON”, I mean, don’t I need to create two setpoint for the coil?



Thanks for your help!



Fabiano Ferreira




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.� Limit attachments to small files.

EnergyPlus Documentation is searchable.� Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31289/stime=1392309367>

<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlaHJ0bGFmBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5MjMwOTM2Nw-->Visit Your Group
* <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmY3UxdXFuBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTIzMDkzNjc-?o=6>New Members 6
<http://groups.yahoo.com/;_ylc=X3oDMTJkMjN2cGdiBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzkyMzA5MzY3><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
� <http://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy � <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe � <http://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___