Re: your humidity problem with DOAS... I have noticed that it is important that the sensible AND latent heat recovery device be bypassed when zone humidity is greater than the outdoor air humidity. It crops up again and again because users don't use the outdoor air mixing object when setting up a DOAS and therefore loose the heatrecovery bypass functionality associated with the outdoor air controller object's economizer functionality. My advice is to setup 100% DOAS as if there is a mixing chamber that you may want to use one in a while (such as early morning warmup from setback). It is more realistic and offers the full set of control options. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 16.06.2014, at 08:30, "puranik.sanket@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |