[EnergyPlus_Support] Re: Regarding the problem of Cooling Coil sizing





I get this warning even if both the "gross rated total cooling capacity" and the "rated air flow rate" are autosized, e.g.:

Coil:Cooling:DX:SingleSpeed,
    Air Loop Blocco principale:Area prep AHU/1 Unitary Cooling Coil DX Cooling Coil,  !- Name
    2,                       !- Availability Schedule Name
    autosize,                !- Gross Rated Total Cooling Capacity {W}
    autosize,                !- Gross Rated Sensible Heat Ratio
    3.00,                    !- Gross Rated Cooling COP {W/W}
    autosize,                !- Rated Air Flow Rate {m3/s}
    773.300000,              !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)}
    Air Loop Blocco principale:Area prep AHU/1 Heating Coil Air Outlet Node,  !- Air Inlet Node Name
    Air Loop Blocco principale:Area prep Supply Side Outlet 1,  !- Air Outlet Node Name
    JCI J05XP Cooling CAPFTemp,  !- Total Cooling Capacity Function of Temperature Curve Name
    JCI J05XP Cooling CAPFFF,!- Total Cooling Capacity Function of Flow Fraction Curve Name
    JCI J05XP Cooling EIRFTemp,  !- Energy Input Ratio Function of Temperature Curve Name
    JCI J05XP Cooling EIRFFF,!- Energy Input Ratio Function of Flow Fraction Curve Name
    JCI J05XP Cooling PLFFPLR,  !- Part Load Fraction Correlation Curve Name
    0.0,                     !- Nominal Time for Condensate Removal to Begin {s}
    0.0,                     !- Ratio of Initial Moisture Evaporation Rate and Steady State Latent Capacity {dimensionless}
    0.0,                     !- Maximum Cycling Rate {cycles/hr}
    0.0,                     !- Latent Capacity Time Constant {s}
    ,                        !- Condenser Air Inlet Node Name
    AirCooled,               !- Condenser Type
    0.90,                    !- Evaporative Condenser Effectiveness {dimensionless}
    autosize,                !- Evaporative Condenser Air Flow Rate {m3/s}
    0

__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___