Ditto in France, 28°C is the max.
European norm EN 1264 says 29°C (edge surfaces at 35°C, bathroom at ti+9=33°C with ti=24°C), which seems to be also the case in north america (recommends below 85°F/29.4°C)
2014-06-27 15:38 GMT+02:00 'jeannieboef@xxxxxxxxx'
jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
Actually, Ned, the sensitive Germans often complain of swollen feet due to floor heating. Here we like to keep the surface temps below 28 deg C.
Mit freundlichen Grüßen- Sent from my iPhone (excuse the brevity)
I’ll take a quick shot in the dark based on my own experience this winter with my home radiant system. The temperature you are setting for radiant may be the fluid temperature (I have used radiant surfaces in Energy+,
but not radiant floor heat systems). I expected my system to work with a fluid temperature in the range of 50C. Good thing I didn’t rip out my electric baseboard, because I couldn’t keep the room warm. My wood floor is too insulation even with Al heat plates
around my Pex pipe. I found I needed to run 80C fluid to stay warm. With that temperature, my floor surface was not much above 32C. I think you should check the floor surface temperature that you have. If you are not reaching mid 30’s, you haven’t given
the system enough power.
Ned Lyon, P.E. (MA, WV)
Staff Consultant
SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct
617.285.2162 mobile
781.907.9009 fax
www.sgh.com
Thanks Jean. 17 C is VAV air temperature reset in winter. In summer, we use 13C for cooling. In winter, we dont want to heat the air too much because there will be core zones that still need cooling, so we use
17 C. Also, we dont want to supply air temperature too high in winter because radiant system will have direct radiation to people and they will feel too hot if we supply air temperature at 30 C. So basically, DOAS can only provide cooling, and radiant will
pick up the rest of the cooling load in summer and all the heating load in winter except the ventilation preheat to 17C from the VAV main heating coil.
I agree there will be a limit posed by the total surface area of radiant system. But i tried with E+ example file and they also have the same problem. I wonder if they under predict the convective heat transfer too much so the air temperature wont go up in
winter and down in summer.
HJ
Biggest tip for radiant systems is to control the surface temperatures. If they are correct, and you still get unmet loads, then you need an additional surface area or auxillary equipment in the zone like a fancoil. The convective and radiative heat transfer
is ABSOLUTELY limited by the amount of area at temperature in the active surface. Check with hand calculations what W/m2 you can expect and if it is enough to meet your loads.
Why is your limit of 17 deg C imposed? If outdoors is warm and you need heating inside, you could use warmer air, no?
Mit freundlichen Grüßen- Sent from my iPhone (excuse the brevity)
Thanks Ery,
I used sized by ventilation because I want to use DOAS to provide ventilation only (at 13-17C all time) and use radiant system to provide the rest of heating and cooling. I also set the priority in zone:equipment to let DOAS meet the load first and then use
radiant to meet the rest of the load. However, there are still tons of unmet load hours and the energy also seems to be higher than using VAV system alone. I also tried with radiant system without DOAS, so I only need to meet the building load, but still I
have tons of unmet load hours. Do you have any sample files that you could share with the group? I would really appreciate if you could let us know how you set the parameter. Seems like there are other people having the same problems too. Maybe I did something
wrong with the zone:sizing or system:sizing tab?
Thanks,
HJ
HJ
You need to play with a number of parameters in Sizing:System and
Controller:OutdoorAir objects for your DOAS system.
If you size your DOAS on "ventilation" then there will be excess
heating and cooling that cannot be met. You can see this in the HTML
report under unmet hours. But if you changet the sizing to "sensible",
all of the excess heating and cooling will be met by the DOAS.
You need to set the equipment connection to set the priority on
heating and cooling of the zone between the radiant and the DOAS.
If you have big DOAS coils as the result of your autosize calculation,
you need to say "No" to 100% OA when cooling and cooling. With this
setting, you will have DOAS most of the time but when there is extra
heating and cooling beyond the ventilation load, then the OA fraction
will be reduced to meet the load.
Ery
On Tue, 24 Jun 2014, HJ
wanghaojie630@xxxxxxxxx [EnergyPlus_Support] wrote:
> Hi all,
>
> I have some projects that has radiant system with DOAS. I find
> EnergyPlus could not size this type of system properly it never try to
> meet the thermostat temeprature. When I look at the summer or winter
> design condition, the temperature could go as high as 30 or as low as 7.
> I used openstudio to export to EnergyPlus. For radiant system, it does
> not use thermostat but use its only temperature control, I wonder if
> that could be the problem for sizing? Does anyone have any successful
> experience with this type of system sizing and could share your idf file?
>
> Many thanks,
>
> HJ
__._,_.___
Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|