|
Hi Karen, as soon as you posted this, I went to test it, because it messes up my current understanding of the autosizing in e+. For Germà n's case, it does not work and fits my current mental model. For HJ's case, it would work as long as the zone setpoint is able to be corrected by the system's air supply. So if he has a zone heating setpoint of 20 and is trying to heat with 13 C system supply air, it will not size the equipment properly and the issue is the same as Germà n's. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 03.07.2014, at 23:53, "Karen Walkerman kwalkerman@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |