Thanks Jean. So for example, if I have heating setpoint of 20C. My DOAS is supplying 13 C and the sizing:system is also set as 13 C for central heating, but the sizing:zone heating supply air temperature is set as 30C. Will it properly size the system? The problem is that I have radiant system but the only place I can specify the water temperature is in sizing:plant. From the EnergyPlus engineering reference, it says the sizing:zone will perform first to calculate how much air flow needed based on supply air temperature (specified in sizing:zone) and zone load. Then sizing:system will run to calculate the air system side. Then sizing:plant will run to calculate the plant water flow rate. However, based on this sequence, I think it will not work properly for radiant system. Or maybe they use different procedure for radiant system? Thanks, HJ
__._,_.___ Posted by: HJ <wanghaojie630@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |