[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] No water flow rate in HotWaterHeatingCoil
Dear All,
I am currently modelling a solar desiccant with absorption cooling system. I use a storage tank to store solar hot water and provide the collected hot water to a Hot Water Heating Coil for regenerating the desiccant wheel and to the Absorption Chiller generator respectively. The Storage Tank is located in the Hot Water Use Side Loop Supply Side. And in the Loop Demand Side, there are two branches: the regeneration Hot Water Heating Coil branch and the Absorption Chiller generator branch. I set the loop demand water inlet to 75C and demand water outlet to 60C. And also I set the Loop supply side water flow rate (tank use side design flow rate) to 9.2 kg/s, set the Absorption Chiller generator design hot water flow rate to 4.4 kg/s, and the Hot Water Heating Coil parameters are:
Performance Input Method: NominalCapacity
Rated Capacity: 300 KW
Rated Inlet Water Temp: 75C
Rated Outlet Water Temp: 60C
Rated Inlet Air Temp: 35C
Rated Outlet Air Temp: 50C
Rated Ratio for Air and Water Convection: 0.5
According to these assumptions, I think the Hot Water Heating Coil water maximum flow rate should be 4.8 kg/s, and it should be able to heat the air to 50C regeneration temperature. However, the simulation results show that the water flow rate is zero in the Hot Water Heating Coil, and the Hot Water Heating Coil Capacity is only 35 KW. Also, the loop supply side water flow rate output (storage tank use side) is equal to the Absorption Chiller generator flow rate of 4.4 kg/s, but not 9.2 kg/s that I have set. No errors happened after running the simulation. And all other conditions are satisfied except the zero water flow rate in the Hot Water Heating Coil. Coud any body know why this happened and give me some suggestions to sovle this problem?
Thanks very much!
Best regards
Bruce
__._,_.___
Posted by: Bruce Ma <brucema1988@xxxxxxxxxxxx>
Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov
The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=35427/stime=1448447041>
<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlM3FjcGc4BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQ0ODQ0NzA0MQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmdWUyNTMyBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0NDg0NDcwNDE->New Members 5
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkYzZndXBpBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDQ4NDQ3MDQx><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___