[EnergyPlus_Support] Re: How to model riding pump curve in E+?





Hi Jim and Jean,

Thank you very much for your useful replies, especially Jim's spreadsheet sent over.

Best regards,

Sean

---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jeannieboef@...> wrote :

?
E+ has variable flow and constant flow pumps. The motor and its energy consumption if fictional. Set it up so that the energy usage reflects what you need it to reflect.

Don't confuse variable/constant flow with variable/constant speed. The second refers to the motor, i.e. impeller speed.

On 10 Mar 2016 7:36 pm, "Jim Dirkes jim@... [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Sean,
I recommend using a variable speed pump object and curve coefficients that mimic the pump curve. I attempted to duplicate a sample ASHRAE curve in the attached spreadsheet; this may give you an idea for your own pump and situation.

On Tue, Mar 8, 2016 at 4:43 AM, seanking.1970@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi,


I am modelling a LEED project, and coming across an issue with modelling on "riding pump curve" for hot water pump when using ASHRAE 90.1-2007 App G (G3.1.3.5). I am quite certain the pump should be a constant speed pump but it needs to deliver variable flow by riding the pump curve. How can I really model it in EnergyPlus?


Any advice would be very much appreciated.


Sean




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@...

Website l  LinkedIn

Goodhartâ??s Law: â??Any observed statistical regularity will tend to collapse once pressure is placed upon it for control purposesâ??



__._,_.___

Posted by: seanking.1970@xxxxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___