[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Re: Thermal capacity of walls





Hello Jeremiah,

Heba referred to an Excel spreadsheet you provided. I don’t suppose you wish to share that spreadsheet?

 

 

cid:image003.png@01D09C46.E75BA0D0

Christopher Jones, P.Eng.
Senior Engineer

 

WSP Canada Inc.

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4
T +1 416-644-4226

F +1 416-487-9766

C +1 416-697-0056

 

www.wspgroup.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, May 20, 2016 11:52 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: Thermal capacity of walls

 

 

Dear Heba,  

 

The methods of calculating HC and U are from ASHRAE 90.1. 

 

You can find more materials in the dataset that ships with E+ called HOF materials. 

 

Best- 

 

Jeremiah 



Sent from my iPhone


On May 20, 2016, at 6:26 AM, hassan_kamel77@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Hello Jeremiah Crossett,

 

I had benefited too much from XLS sheet file.

 

Now I have a small problem,

 

I need to use your inputs for the (Asphalt very rough) layer,

How can I cite the numbers in my research??

 

The question in another way,

Where can I find the source of your inputs for different layer materials?!!

 

I am in a bad need for it,

 

Thanks in advance,

Heba

 

 



You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.



__._,_.___

Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___
Email file not found:
C:\Users\lklawrie\Downloads\Embedded\image002122.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00314.jpg
Attachment not found:
C:\Users\lklawrie\Downloads\Embedded\image00422.jpg