[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Fwd: [EnergyPlus_Support] Re: AirTerminal:SingleDuct:ParallelPIU LEED ASHRAE






Hi Francesco,

I change the maximun flow rate in the Fan (The PIU Fan) and also I change the MAximun secondary AirFlow Rate of the AirTerminal:SingleDuct:PIU.
Doing that had help me to avoid getting many set point not met hours. If I leave the Maximum Flow Rate of the Fan:constant Valume as autosize, i would get many unmet load hours.

Prints below may help you!
Imágenes integradas 1
Imágenes integradas 2

2016-07-22 12:34 GMT-05:00 fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

I'm reading this old discussion again because I'm trying to respect G3.1.3.14, in particular: "Fans in parallel VAV fan-powered boxes shall be sized for 50% of the peak design flow rate". 

I'm using this useful James's suggestion:

I do not know of a way to automatically size the PFP fan for 50% of the maximum primary flow rate, so I run the program once using â??autosizeâ?? for primary flow rate, then check to see the autosized value, then enter 50% of that into the fan â??Maximum flow rateâ??.

I used this suggestion also in the past, but now I'm facing a problem. After that I have imposed the "Maximum Secondary Air Flow Rate" of the object AirTerminal:SingleDuct:ParallelPIU:Reheat equal to 50% of the "Maximum Primary Air Flow Rate", the heating setpoint not met hours have increased a lot. It seems reasonable, because in centralized VAV systems with PFP boxes the heating demand is met by the secondary flow rate.

What do you think? Any suggestion, please?

Best Regards
Francesco
 





__._,_.___

Posted by: andres gmail <andresdagm@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___