Re: [EnergyPlus_Support] Re: AirTerminal:SingleDuct:ParallelPIU LEED ASHRAE





Francesco,

Marcus and I agree: 
Perhaps we're understanding some terms differently? "Available" does not mean the fan is actually running in the E+ program; it means that it is permitted to run if needed for temperature control or other reasons.  Have you used output:variables to monitor what is happening?

The Night Cycle Manager has a similar feature. 
Inline image 1
  1. The Applicability Schedule determines when AvailabilityManager:NightCycle is used.
  2. The Fan Schedule identifies the "occupied" and "unoccupied" periods.
  3. Then the :NightCycle control turns on the fan when schedule #1 is "ON", schedule #2 is in  the "unoccupied" period AND the zone needs heating or cooling.
I hope that helps and is not too basic - I think I may be missing part of the reason for your questions.

On Tue, Aug 16, 2016 at 2:40 PM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Here another point of view (Marcus Sheffer): 





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

When shouldering your personal pack of life's burdens, bring a pocket full of grit and a bucket full of joy.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___