Sheffer has suggested the following document (see pp. 3.97-3.98):

http://www.pnnl.gov/main/publications/external/technical_reports/PNNL-25130.pdf

Consider this statement:

â??With parallel style fan-powered VAV boxes, the constant volume terminal unit fan is only on when the primary airflow is at design minimum and the zone temperature is less than 2°F above the heating setpoint schedule.â??

 

Therefore Iâ??m modeling in the following way.

The PIU boxes are always available. The â??Fan On Flow Fractionâ?? is equal to the â??Minimum Primary Air Flow Fractionâ?? (â??the constant volume terminal unit fan is only on when the primary airflow is at design minimumâ??â?¦).

 

AirTerminal:SingleDuct:ParallelPIU:Reheat,

    FloorX09:OXOX1 Parallel PIU,  !- Name

    On,                      !- Availability Schedule Name

    autosize,                !- Maximum Primary Air Flow Rate {m3/s}

    autosize,                !- Maximum Secondary Air Flow Rate {m3/s}

    0.3,                     !- Minimum Primary Air Flow Fraction

    0.3,                     !- Fan On Flow Fraction

    VAV09 Ramificazione di Zona Outlet Node 1,  !- Supply Air Inlet Node Name

    FloorX09:OXOX1 Parallel PIU PIU Secondary From Zone,  !- Secondary Air Inlet Node Name

    FloorX09:OXOX1 Parallel PIU Supply Inlet,  !- Outlet Node Name

    FloorX09:OXOX1 Parallel PIU PIU Mixer Outlet,  !- Reheat Coil Air Inlet Node Name

    FloorX09:OXOX1 Parallel PIU Zone Mixer,  !- Zone Mixer Name

    FloorX09:OXOX1 Parallel PIU Supply Fan,  !- Fan Name

    Coil:Heating:Electric,   !- Reheat Coil Object Type

    FloorX09:OXOX1 Parallel PIU Heating Coil,  !- Reheat Coil Name

    ,                        !- Maximum Hot Water or Steam Flow Rate {m3/s}

    ,                        !- Minimum Hot Water or Steam Flow Rate {m3/s}

    ,                        !- Hot Water or Steam Inlet Node Name

    0.0010;                  !- Convergence Tolerance

 

The PIU fans are never available, but they turn on if it is requested by the heating demand (nightcycle):

 

Fan:ConstantVolume,

    FloorX09:OXOX1 Parallel PIU Supply Fan,  !- Name

    Off 24/7,                !- Availability Schedule Name

    0.825,                   !- Fan Total Efficiency

    610,                     !- Pressure Rise {Pa}

    autosize,                !- Maximum Flow Rate {m3/s}

    0.90,                    !- Motor Efficiency

    1.00,                    !- Motor In Airstream Fraction

    FloorX09:OXOX1 Parallel PIU PIU Secondary From Zone,  !- Air Inlet Node Name

    FloorX09:OXOX1 Parallel PIU Supply Fan Outlet,  !- Air Outlet Node Name

    PIU Supply Fan;          !- End-Use Subcategory

 

As â??Thermostat Toleranceâ?? Iâ??m using a negative value because â??? and the zone temperature is less than 2°F above the heating setpoint scheduleâ?? (2°F is about 1°C). Actually, if I consider the results it seems that a negative value is considered like 0.

 

AvailabilityManager:NightCycle,

    VAV09 UTA Ciclo Operativo Notturno 2,  !- Name

    On 24/7,                 !- Applicability Schedule Name

    Off 24/7,                !- Fan Schedule Name

    CycleOnAnyZoneFansOnly,  !- Control Type

    -1,                      !- Thermostat Tolerance {deltaC}

    3600;                    !- Cycling Run Time {s}

 

Moreover, Iâ??m using a AvailabilityManager:NightCycle object to control the cooling demand during unoccupied hours.



__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___