[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: HeatExchanger:Desiccant:BalancedFlow wrong temperature and humidity results





Hi again !

To be more accurate about my problem, I join the performance data of the Desiccant object.

For instance, with the following points and the performance datas attached:
RWI (Regen Water ratio Inlet) = 12 g/kg
RTI (Regen Temperature Inlet) = 70 °C
PWI (Process Water ratio Inlet) = 15 g/kg
PTI (Process Temperature Inlet) = 34 °C

Energyplus simulation gives me the following outlets:
RWO (Regen Water ratio Outlet) = 18.5 g/kg
RTO (Regen Temperature Outlet) = 43.4 °C
PWO (Process Water ratio Outlet) = 8.5 g/kg
PTO (Process Temperature Outlet) = 60.5 °C

whereas equations to find RWO and RTO given by the Engineering Reference document give me:
RWO (Regen Water ratio Outlet) = 21.2 g/kg
RTO (Regen Temperature Outlet) = 29.1 °C
PWO (Process Water ratio Outlet) = 5.7 g/kg
PTO (Process Temperature Outlet) = 74.9 °C

The mass flow rate was 2100 m3/h (balanced)

Is there a problem in Performance Data ?

Best Regards
TM


__._,_.___

Posted by: tommathelin@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment Converted: "D:\Eudora\Attach\DEC rotor Energyplus.idf"