Joe,

The coupling between EnergyPlus and CONTAM is the quasi-dynamic (so-called ping-pong), and is based on the Functional Mock-up Interface for Co-simulation specification.
The aforementioned journal article addresses the limitations of the quasi-dynamic method which does benefit from shorter time steps, and it also presents a comparison with the Airflow Network model (AFN).
We have applied the coupled modeling to a net zero residential model and a few of the DOE commercial reference buildings with very promising results.


Poppendieck, D., S. Khurshid, W. S. Dols, L. C. Ng, B. J. Polidoro and S. J. Emmerich (2016). Formaldehyde Concentrations in a Net-Zero Energy House: Real-time Monitoring and Simulation. Indoor Air 2016. Ghent, Belgium.



Ng, L. C., D. Poppendieck, W. S. Dols and S. J. Emmerich (2016). Evaluating IAQ and Energy Impacts of Ventilation in a Net-Zero Energy House Using a Coupled Model. IAQ 2016. Alexandria, VA, ASHRAE and AIVC.


However, the CONTAM3DExport can also be used to create IDF geometry, albeit for rectilinear configurations, with fairly robust results.
It can also be used to generate the AFN sub-surfaces that can be somewhat cumbersome to create.
Once one has the IDF file with geometry, they can modify it with SketchUp/OpenStudio, IDF Editor, etc.

Of course I may be biased, but I believe the ContamW interface is not that difficult to master for the purposes of generating these building models.


- Stuart



From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Thursday, December 08, 2016 9:20 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model





Stuart,

That's interesting information!� Does running CONTAM3DExport result in a tighter or a looser coupling between EnergyPlus and the airflow modeling?� When I worked on the first implementation of an airflow model (COMIS) into EnergyPlus back in the day, it was what Jan Hensen would call a "ping-pong" and not an "onion" approach.�� One of the dirty secrets from my work was finding that the solutions would oscillate by time step.� I had proposed making the link a half-onion (??) , i.e., redo the thermal calculation using the air flows computed by the air flow modeling, but unfortunately my funding got cut just at that point.�

Joe

Joe Huang<o:p></o:p>
White Box Technologies, Inc.<o:p></o:p>
346 Rheem Blvd., Suite 205A<o:p></o:p>
Moraga CA 94556<o:p></o:p>
<a href="mailto:yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx";>yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx</a><o:p></o:p>
<a href="http://weather.whiteboxtechnologies.com";>http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p>
(o) (925)388-0265<o:p></o:p>
(c) (510)928-2683<o:p></o:p>
&quot;building energy simulations at your fingertips&quot;<o:p></o:p>
On 12/8/2016 12:38 PM, 'Dols, William Stuart (Fed)' <mailto:william.dols@xxxxxxxx> william.dols@xxxxxxxx [EnergyPlus_Support] wrote:

> �

> NIST, the developers of CONTAM, have also enable the coupling of CONTAM with EnergyPlus directly.
> This coupling features a tool, CONTAM3DExport, that you can use to generate an EnergyPlus model from a CONTAM model.
> The process is documented in the “Working with EnergyPlus” section of the CONTAM User Guide.
> CONTAM3DExport can be used to generate an Airflow Network Model as well.
> See the following reference:
> Dols, W. S., S. J. Emmerich and B. J. Polidoro (2016). "Coupling the Multizone Airflow and Contaminant Transport Software CONTAM with EnergyPlus using Co-simulation." Building Simulation 9: 469-479.

> �

> CONTAM and associated tools are available from the website that Joe mentioned.
> <http://www.bfrl.nist.gov/IAQanalysis/software/index.htm>> http://www.bfrl.nist.gov/IAQanalysis/software/index.htm
> 
> 
> 
> - Stuart

> 
> W. Stuart Dols
> National Institute of Standards and Technology
> Engineering Laboratory
> Indoor Air Quality and Ventilation Group
> 100 Bureau Drive MS 8633
> Gaithersburg, MD 20899-8633
> 301-975-5860
> <http://www.bfrl.nist.gov/IAQanalysis>> www.bfrl.nist.gov/IAQanalysis

> �

> From: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx [<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
> Sent: Thursday, December 08, 2016 2:31 PM
> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model

> �

> The EnergyPlus documentation should explain the IDF objects that are used for the multi-zone air-flow modelling, which are very much tied to the thermal modeling of the building, i.e., walls, windows, doors, etc., except that instead of defining their thermal properties you are defining their air-flow properties, such as leakage area, and in the case of windows their operating schedules.

> Bear in mind that EnergyPlus is using the AIRNET program to do the multi-zone air flow modeling. If you want more information about this that you don't find in the EnergyPlus documentation, you could also look at the CONTAM User Manual (<http://www.bfrl.nist.gov/IAQanalysis/CONTAM/userguide.htm>www.bfrl.nist.gov/IAQanalysis/CONTAM/userguide.htm ).� CONTAM is the successor program to AIRNET with a user-friendly GUI added.

> Joe

> Joe Huang<o:p></o:p>
> White Box Technologies, Inc.<o:p></o:p>
> 346 Rheem Blvd., Suite 205A<o:p></o:p>
> Moraga CA 94556<o:p></o:p>
> <a href="mailto:yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx";>yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx</a><o:p></o:p>
> <a href="http://weather.whiteboxtechnologies.com";>http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p>
> (o) (925)388-0265<o:p></o:p>
> (c) (510)928-2683<o:p></o:p>
> &quot;building energy simulations at your fingertips&quot;<o:p></o:p>
> On 12/8/2016 9:46 AM, 'Edward G. Lyon' <mailto:eglyon@xxxxxxx>eglyon@xxxxxxx [EnergyPlus_Support] wrote:

>> �

>> Although perhaps a bit more effort, you could also look at ODS Studio.� This Australian group has levered Blender as a graphic interface, OpenFoam as a CFD tool, and E+ as a calculation engine.� Mark Pitman has written some C++ modules and Python code to assist in generating airflownetwork models for E+ analysis.� There are some video demonstrating the code that may help you understand the general process, even if you go in a different direction to generate the model.� I use this software for all our airflownetwork models, though I usually export the IDF at a geometry and network state and finish it with other editors.� That said, it is a complex process that is not as simple as Mark makes it look.� Geometry errors can creep into the model and thwart Mark’s Python code. Good luck�

>> �

>> Ned Lyon, P.E. (MA, WV)
>> Staff Consultant

>> SIMPSON GUMPERTZ & HEGER
>> 781.907.9000�main
>> 781.907.9350 direct�
>> 617.285.2162 mobile�
>> 781.907.9009�fax
>> <http://www.sgh.com>>> www.sgh.com
>> 
>> <https://infoexchange.sgh.com/UserWeb/Transfers/PersonalTransfer.aspx?personal=EGLyon@xxxxxxx>>> Send Files

>> From: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx [<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
>> Sent: Thursday, December 08, 2016 12:20 PM
>> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
>> Subject: Re: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model

>> �

>> �

>> I'm sorry, I cannot.� All I can suggest is to look at the example files that come installed with E+ and to read the documentation.� You also might consider posting your question on <http://unmethours.com>unmethours.com

>> �

>> �

>> �

>> On Thu, Dec 8, 2016 at 11:46 AM, bhavana patil <mailto:ana5patil@xxxxxxxx>ana5patil@xxxxxxxx [EnergyPlus_Support] <<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

>>> �

>>> Hi,

>>> Thanks for the reply. Can you please suggest me good resource to learn air flow network

>>> method? I am reading InputOutputReference document. I will really appreciate.�

>>> �

>>> From: "<mailto:allinson_louis@xxxxxxxxxxx>allinson_louis@xxxxxxxxxxx [EnergyPlus_Support]" <<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx>
>>> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
>>> Sent: Thursday, December 8, 2016 3:56 PM
>>> Subject: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model

>>> �

>>> �

>>> Hi

>>> �

>>> No you cannot assume 3 ACH. Natural ventilation airflow is dependent on buoyancy driven (caused by internal/external temperature difference) and wind driven. These vary transiently and therefore you will not be delivering a constant ventilation rate, even if you are controlling the vent.

>>> �

>>> ideally you want to use the airflow network to model airlfow through the windows. You also want to then control the window openings such that you deliver the necessary airflow for IAQ (CIBSE guide B recommends 10l/s/person) when occupied and the sufficient airflow to mitigate overheating.

>>> �

>>> i suggest that you read section Group - airflow network in the inputoutput document

>>> �

>>> you could also use an interface like DesignBuilder and read their help files on modelling ventilation through a window

>>> �

>>> �

>>> kind regards

>>> �

>>> �

>>> �

>>> �

>> �

> �







__._,_.___

 Posted by: "Dols, William Stuart (Fed)" <william.dols@xxxxxxxx>

EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
<http://www.energyplus.net/>http://www.energyplus.net/

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.� Limit attachments to small files.

EnergyPlus Documentation is searchable.� Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.

<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=37143/stime=1481292599>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJla2pqc3JnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQ4MTI5MjU5OQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmbHVoZDd0BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0ODEyOTI1OTk->New Members 11
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkbGJ0OHZxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDgxMjkyNTk5><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
� <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy � <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe � <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___