[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: CentralHeatPumpSystem with one chiller/heater [2 Attachments]





I think the problem is the relationship among the three loops:

-         - Chilled water loop

-         - Hot water loop

-       --  Aquifer loop

In all those loops the CentralHeatPumpSystem is present.

In the aquifer loop Iâ??m using PlantComponent:TemperatureSource (constant and equal to 13°C)

Iâ??ve found no example file where both PlantComponent:TemperatureSource and CentralHeatPumpSystem are present.

Some doubts:

-1.    -   For the aquifer loop is PlantLoop or the CondenserLoop object the best solution?

2.     - Which kind of setpoint manager (scheduled?) shall be used? With which value (the same temperature of the temperaturesource, i.e. 13°C?)?

-3.    - Which kind of Plant Equipment Operation scheme shall be used? PlantEquipmentOperation:Uncontrolled?

4.      - Other input data to which I should pay attention?


Now I have replaced the PlantLoop with the CondenserLoop and the system works also in chiller mode, but only in winter... When I used the PlantLoop it was never working in chiller mode.


Here some parts of the model now:

 

CentralHeatPumpSystem,

    ChillerBank,             !- Name

    SmartMixing,             !- Control Method

    Raffreddamento Pompa di Calore CHW Inlet Node,  !- Cooling Loop Inlet Node Name

    Raffreddamento Pompa di Calore CHW Outlet Node,  !- Cooling Loop Outlet Node Name

    Pompa di Calore Condenser Inlet Node,  !- Source Loop Inlet Node Name

    Pompa di Calore Condenser Outlet Node,  !- Source Loop Outlet Node Name

    Riscaldamento Pompa di Calore HW Inlet Node,  !- Heating Loop Inlet Node Name

    Riscaldamento Pompa di Calore HW Outlet Node,  !- Heating Loop Outlet Node Name

    460,                     !- Ancillary Power {W}

    ,                        !- Ancillary Operation Schedule Name

    ChillerHeaterPerformance:Electric:EIR,  !- Chiller Heater Modules Performance Component Object Type 1

    ChillerHeaterModule 1,   !- Chiller Heater Modules Performance Component Name 1

    ON,                      !- Chiller Heater Modules Control Schedule Name 1

    4;                       !- Number of Chiller Heater Modules 1

 

PlantLoop,

    aquifer loop,            !- Name

    Water,                   !- Fluid Type

    ,                        !- User Defined Fluid Type

    Circuito di Condensazione Funzionamento,  !- Plant Equipment Operation Scheme Name

    Circuito di Condensazione Supply Side Outlet,  !- Loop Temperature Setpoint Node Name

    50,                      !- Maximum Loop Temperature {C}

    5,                       !- Minimum Loop Temperature {C}

    autosize,                !- Maximum Loop Flow Rate {m3/s}

    0.001,                   !- Minimum Loop Flow Rate {m3/s}

    autocalculate,           !- Plant Loop Volume {m3}

    Circuito di Condensazione Supply Side Inlet,  !- Plant Side Inlet Node Name

    Circuito di Condensazione Supply Side Outlet,  !- Plant Side Outlet Node Name

    Circuito di Condensazione Rami del lato di Alimentazione,  !- Plant Side Branch List Name

    Circuito di Condensazione Connessioni del lato di Alimentazione,  !- Plant Side Connector List Name

    Circuito di Condensazione Demand Side Inlet,  !- Demand Side Inlet Node Name

    Circuito di Condensazione Demand Side Outlet,  !- Demand Side Outlet Node Name

    Circuito di Condensazione Rami del Lato della Domanda,  !- Demand Side Branch List Name

    Circuito di Condensazione Connessioni del Lato della Domanda,  !- Demand Side Connector List Name

    Optimal,                 !- Load Distribution Scheme

    Circuito di Condensazione Lista dei Manager di Disponibilitଠ !- Availability Manager List Name

    ,                        !- Plant Loop Demand Calculation Scheme

    None,                    !- Common Pipe Simulation

    None;                    !- Pressure Simulation Type

 

PlantEquipmentOperationSchemes,

    Circuito di Condensazione Funzionamento,  !- Name

    PlantEquipmentOperation:Uncontrolled,  !- Control Scheme 1 Object Type

    Circuito di Condensazione Scheme 1,  !- Control Scheme 1 Name

    On 24/7;                 !- Control Scheme 1 Schedule Name

 

PlantEquipmentOperation:Uncontrolled,

    Circuito di Condensazione Scheme 1,  !- Name

    Circuito di Condensazione Scheme 1 Equipment List;  !- Equipment List Name

 

PlantEquipmentList,

    Circuito di Condensazione Scheme 1 Equipment List,  !- Name

    PlantComponent:TemperatureSource,  !- Equipment 1 Object Type

    FluidSource;             !- Equipment 1 Name

 

NodeList,

    Circuito di Condensazione Setpoint Manager Node List,  !- Name

    Circuito di Condensazione Supply Side Outlet;  !- Node 1 Name

 

SetpointManager:Scheduled,

    Circuito di Condensazione Setpoint Manager,  !- Name

    Temperature,             !- Control Variable

    15C,                     !- Schedule Name

    Circuito di Condensazione Setpoint Manager Node List;  !- Setpoint Node or NodeList Name

 

PlantComponent:TemperatureSource,

    FluidSource,             !- Name

    Scambiatore di Calore Geotermico Water Inlet Node,  !- Inlet Node

    Scambiatore di Calore Geotermico Water Outlet Node,  !- Outlet Node

    0.0045,                  !- Design Volume Flow Rate {m3/s}

    Constant,                !- Temperature Specification Type

    13;                      !- Source Temperature {C}

 

A strange result (actually, I get many strange results): as you can see in the attached images, in the results the â??Chiller Heater System Source Mass Flow Rateâ?? is different from the water flow rate through the condenser (the second one is constantly equal to 0!). I thought they were the same.

 

Thanks

Best Regards

Francesco



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <fpasserini.tn@...> wrote :

"Properly" should mean that E+ is using the â??actual chilled water temp and actual condenser water temp. Is that the case? 
It's using the "Performance Curve Input Variable 1 Value", the "Performance Curve Input Variable 2 Value" and the parameters defined in the curve to calculate the "Performance Curve Output Value". The problem is that it is not using the correct value of "Performance Curve Input Variable 1 Value", in my opinion. So, wrong input -> wrong output (sorry, I was not clear).
Is the setpoint manager value different than the "reference" temperature?â??
Yes, 
â??Reference Cooling Mode Leaving Chilled Water Temperatureâ?? = 6.7°C
setpoint manager temperature = 6°C
for CHILLERHEATERCLGCAPFT it's using 6.7°C
for CHILLERHEATERCLGEIRFT it's using 6.0°C
In both cases I would expect the temperature from the dynamic simulation, which is higher (15-16°C), because the system is not working properly.
You'll need to determine why the chiller does not operate for more than one hour. That may â??be part of the reason for the curve output problem.
Ok. Actually I was thinking in the other way: the chiller/heater doesn't operate properly, is the problem relative to the curves (or to the points of the curves where the system is operating)?


---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

Francesco,
Comments below...

On Mon, Jul 3, 2017 at 8:46 AM, fpasserini.tn@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello, Jim
The source/condenser temperature is constant because the PlantComponent: TemperatureSource object is used.
The calculated output is constant. I have recalculate the output in excel, considering the parameters used for the curve, and the polynomial formula is calculated by EnergyPlus properly.  
â??"Properly" should mean that E+ is using the â??actual chilled water temp and actual condenser water temp. Is that the case? 
The strange issue is that the leaving chilled water temperature used in the calculation is not taken from the dynamic simulation but it is the â??Reference Cooling Mode Leaving Chilled Water Temperatureâ??.
â?? Is the setpoint manager value different than the "reference" temperature?â??
I have plotted the â??Cooling Mode Electric Input to Cooling Output Ratio Function of Temperatureâ?? (CHILLERHEATERCLGEIRFT) too and Iâ??m attaching it now. As for that curve, the temperature 6°C, which is the setpoint manager temperature, is considered as leaving chilled water temperature!?
As you can see in the second picture, the chiller-heater is working in cooling mode only one hour. Therefore the setpoint manager temperature is not met.
â?? You'll need to determine why the chiller does not operate for more than one hour. That may â??be part of the reason for the curve output problem.
Best Regards




--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, GR, MI 49504

(alphabet soup of efforts for excellence: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@...

Website l  LinkedIn

Coffee conversation: They love truth when it enlightens them, they hate truth when it accuses them? They love truth when it reveals itself, and hatte it when it reveals them.

.

 


__._,_.___
View attachments on the web

Posted by: fpasserini.tn@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment Converted: "D:\Eudora\Attach\sourcemassflowrate.png" Attachment Converted: "D:\Eudora\Attach\condenserinletnode.jpg"