|
If you model the AIRCOOLED Chiller:Electric :EIR without using the input for Condenser Fan Power Ratio, then condenser fan power is included in the chiller power/energy calculation. If you enter a value for Condenser Fan Power Ratio then the condenser fan power will be calculated separately and reside on a cooling plant electricity meter (and so other inputs, COP, curves, etc. should not include condenser fan power). The former will model variable speed condenser fans while the latter will model a single-speed condenser fan(s). Chiller:Electric:EIR, 0.01, !- Condenser Fan Power Ratio {W/W} Then in the mtd you should see the condenser fan electric energy on the cooling plant meter. On 4/24/2018 12:50 PM, Jim Dirkes
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
-- Richard Raustad Florida Solar Energy Center http://evtc.fsec.ucf.edu/ __._,_.___ Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |