Yes, this is an odd thing to do. If you supply air to a zone with absolutely no load, the return should equal the zone conditions. So if you get the zone load for the next time step, you should be able to set the supply conditions to
meet the load. Not sure if that is doable in EMS or not, and it likely creates chaos for the mechanical system simulation. Aside from that, I see no real world situation where this would occur. The closest I can think of is some museum system I have designed where all the envelope loads are introduced into the return air flowing through the exterior wall cavity.
Essentially one supplies conditioned air to the zone at design conditions and the load hits the system after air goes into the zone return duct, except of course for people and lighting in the space. It seems one could come close to that with the return air
plenum configuration. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Salut Pauline, I'm unclear what's your actual goal, but if I understand correctly you just want to force the return conditions to be constant and don't care about how/which component is actually altering the conditions (and the energy use associated with
it). I checked the actuators available for the EnergyManagementSystem, thinking there could be a way to force the conditions on the zone return air node or the loop's return air node, but I couldn't find a way to do that... The next thing I was thinking of, which was quite convoluted, was to use a dummy zone downstream and set it up as a plenum. This zone would be conditioned by something like ZoneHVAC:UserDefined (EMS program to set up return conditions...).
But now I seem to recall that a plenum zone cannot have any equipment in it. So back to square zero.... I think the simpler solution (... sic!) here would be to add an override in the source code and recompile. Perhaps you could explain what you're actually trying to do and we might come up with a better alternative/workaround. Best, Julien
2018-07-19 11:53 GMT+02:00
pauline.couvrat@xxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
__._,_.___ Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |