|
Christopher,
The zone average %RH sounds like it would be pretty darn close to me. (closer by far than "not possible"). If the Baseline and Proposed models apply the same method, the comparison should be spot on, I think.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, March 4, 2019 8:08 AM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Cc: Jim Dirks Subject: [EnergyPlus_Support] RE: EnergyPlus humidification control Thank you Jim, Given that the return air stream may include pick-up from the lights, would not the return RH be slightly less than the average zone RH? It likely wouldn’t be significant.
Christopher R Jones, P.Eng. T+ 1 416-644-0252
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Christopher, I'd suggest that the modeler use: - for a multiple zone system: SetpointManager:MultiZone:MinimumHumidity:Average - for a single zone system: SetpointManager:SingleZone:Humidity:Minimum
"Officially", E+ is not measuring humidity at the return air node, but it's doing effectively the same thing by determining the zone return air humidity. From:
EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of 'Jones, Christopher'
christopher.r.jones@xxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>
I am reviewing a LEED 2009 submission. The design sequence of operations calls for humidification to be controlled by measuring the return air stream RH. The modeler states that it is not possible for EnergyPlus v9.0 to model this control strategy. Is this the case? I am used to IES where it is possible with a few clicks.
Christopher R Jones, P.Eng. T+ 1 416-644-0252
__._,_.___ Posted by: Jim Dirkes <Jim@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |