[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Is it possible to model in EnergyPlus window ventilation triggered by the history of A/C operations the previous X number of days?





Joe,

EMS tends to be intimidating the first time you use it, but you'll soon realize it's not very complicated, it's just limited by the actuators you can use (and sometimes the workarounds you have to think about when there isn't the perfect actuator to use). The calling points are sometimes hard to figure out too. But as long as you look closely at the outputs it produces you should be fine.

For your use case, you'll have to look at the eplusout.edd and look at the actuators defined for your ventilation object. Keep in mind that all schedules also have a schedule value actuator, so setting the value of an availability schedule could be one of your best bets too. When actuating things one thing to be mindful of is what happens during sizing (typically it'll use whatever default is defined, but wont use the EMS program).

If you get stuck when actually implementing your program, drop a line and I'm sure the list will help.

Good luck,
Julien

--
Sent from a mobile device, please excuse the brevity.

Julien Marrec, EBCP, BPI MFBA
Owner

Direct: +33 6 95 14 42 13
Website: www.effibem.com
LinkedIn (en) | (fr)
On Jun 10, 2019, at 04:42, "Joe Huang YJHuang@xxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <energyplus_support@xxxxxxxxxxxxxxx> wrote:
 

Julien,

Thank you.  This is very helpful, since my knowledge of EnergyPlus has been basically dormant since 2005, when I was last part of the development team. I only know of EMS from its mention by others, but haven't a clue how to use it.  Now that you've given me a mock-up,  I'll have to look at the documentation to make sense of it.  I don't know about others' experience, but for me working examples are always much more helpful than reading the documentation :-)

Joe

On 6/9/2019 3:30 PM, Julien Marrec julien.marrec@xxxxxxxxx [EnergyPlus_Support] wrote:
 
Joe,

You'll find in attachment a file that shows the gist. I took the E+ Example file WindACAuto.idf and added a simple EMS program to compute the @TrendSum over 384 timesteps = 4 days (at 4 timesteps/hours).

The interesting bit is right at the end.

Hope that helps,
Julien

--
Julien Marrec, EBCP, BPI MFBA
Owner at EffiBEM
T: +33 6 95 14 42 13

LinkedIn (en) | (fr) :


Le dim. 9 juin 2019 à 23:42, Julien Marrec < julien.marrec@xxxxxxxxx> a écrit :
Hi  Joe,

I am unaware of something built-in but it's certainly possible via EMS.
You'd use a trend variable on an ems sensor like "cooling power W" or On/Off status (whichever variable on your specific cooling object that will serve as a proxy for cooling operation).
In your EMS program you can do a @Sum (or @max...) on your trend variable for the past N timesteps and check if > 0, meaning the AC would have been on during that time.

Hope that helps,
Juliem

--
Sent from a mobile device, please excuse the brevity.

Julien Marrec, EBCP, BPI MFBA
Owner

Direct: +33 6 95 14 42 13
Website:  www.effibem.com
LinkedIn ( en) | ( fr)
On Jun 9, 2019, at 12:08, "Joe Huang YJHuang@xxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" < energyplus_support@xxxxxxxxxxxxxxx> wrote:
 

My apologies if my question in the subject line seems unclear. I've been having
difficulties getting good correspondence in residential runs done with DOE-2.1E to doing
them with EnergyPlus, with EnergyPlus showing more than twice the Heating Energy as shown
by DOE-2.1E.  By process of elimination, I've narrowed down the discrepancy to how natural
ventilation through windows is being modeled. These runs are  in California climates where
overcooling by natural ventilation during the day can substantially increase heating
energy at night during the swing season, leading to the 2X increase over  the entire year.

The natural ventilation model in DOE-2 has a feature that checks whether  the AC had been
on for the previous X number of days.  If so, the program then knows that it's the cooling
season, and will then permit window ventilation based on either temperature or enthalpy
difference between the indoor and the outdoor.   If the check finds there was no cooling
the previous X number of days, it then knows it's not in the cooling season and window
ventilation is not permitted. For those who are curious, the actual BDL inputs are as follows:

 VTSCH     SCHEDULE  $Vent schedule based on previous 4 days load
                    THRU MAY 14 (ALL) (1,24) (-4)
                    THRU SEP 30 (ALL) (1,24) (-4)
                    THRU DEC 31 (ALL) (1,24) (-4) ..
VOPSCH    SCHEDULE  $Vent operation schedule
                    THRU DEC 31 (ALL) (1,24) (VTYPE) ..    (where VTYPE =1 for
temperature difference, -1 for enthalpy difference, 0 for no ventilation)
WINDOPER  SCHEDULE  $No window operation between 11 p.m. and 6 a.m..
                   THRU DEC 31 (ALL) (1,6)  (0.0)
                                        (7,23) (1.0)
                                      (24)   (0.0)  ..

I've looked into my EnergyPlus idf and found this:

  Controller:OutdoorAir,
    SYS OA Controller,       !- Name
    SYS Relief Air Outlet,   !- Relief Air Outlet Node Name
    SYS Air Loop Inlet,      !- Return Air Node Name
    SYS Mixed Air Outlet,    !- Mixed Air Node Name
    SYS Outside Air Inlet,   !- Actuator Node Name
    autosize,                !- Minimum Outdoor Air Flow Rate {m3/s}
    autosize,                !- Maximum Outdoor Air Flow Rate {m3/s}
    DifferentialDryBulb,     !- Economizer Control Type
    ModulateFlow,            !- Economizer Control Action Type
    ,                        !- Economizer Maximum Limit Dry-Bulb Temperature {C}
    ,                        !- Economizer Maximum Limit Enthalpy {J/kg}
    ,                        !- Economizer Maximum Limit Dewpoint Temperature {C}
    ,                        !- Electronic Enthalpy Limit Curve Name
    ,                        !- Economizer Minimum Limit Dry-Bulb Temperature {C}
    LockoutWithCompressor,   !- Lockout Type
    FixedMinimum;            !- Minimum Limit Type

which seems not to have such a load-based toggle.   Is there another Residential or Window
Ventilation Object that I should use?  Or is this something that can be programmed using
EMS? I've sorry if I'm asking a well-known question, but I have simply not followed the
development of EnergyPlus for the past 15 years.

Any advice or suggestions would be appreciated.

Joe



__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___