[EnergyPlus_Support] a strange cooling load
I tested a example for comparison.
The condition of example is same except wall thickness.
One is 0.01m and the other is 0.3m in wall thickness.
But a result is very strange.
First, the cooling load appeared minus or zero although 
outdoor temperature is higher than indoor temperature.
Second, I control the indoor temperature wsing a purchased 
air but air mean temperature differed from a value of input 
purchased air.
Third, the total cooling load appeared zero in some componet.
Please, refer to 'idf' file.
Also this strange results appear when the density is half 
and a wall is composite material.
**** idf file ****
!-Generator IDFEditor 1.05
!-NOTE: All comments with '!-' are ignored by the IDFEditor 
and are generated automatically.
!-      Use '!' comments if they need to be retained when 
using the IDFEditor.
!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
VERSION,
! LGOSQ
! LGOSQ4.IDF;
! 2002-10-30 ¿ÀÈÄ 5:06:37
! LG Electronics Inc.
    1.0.2;                   !- Version Identifier
!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
BUILDING,
    NONE,                    !- Building Name
    0,                       !- North Axis {deg}
    City,                    !- Terrain
    0.04,                    !- Loads Convergence Tolerance 
Value {W}
    0.4,                     !- Temperature Convergence 
Tolerance Value {C}
    MinimalShadowing;        !- Solar Distribution
!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP IN HOUR 
===========
TIMESTEP IN HOUR,
    4;                       !- Time Step in Hour
!-   ===========  ALL OBJECTS IN CLASS: INSIDE CONVECTION 
ALGORITHM ===========
INSIDE CONVECTION ALGORITHM,
    Detailed;                !- InsideConvectionValue
!-   ===========  ALL OBJECTS IN CLASS: OUTSIDE CONVECTION 
ALGORITHM ===========
OUTSIDE CONVECTION ALGORITHM,
    Detailed;                !- OutsideConvectionValue
!-   ===========  ALL OBJECTS IN CLASS: SKY RADIANCE 
DISTRIBUTION ===========
SKY RADIANCE DISTRIBUTION,
    1;                       !- SkyRadianceValue
!-   ===========  ALL OBJECTS IN CLASS: SOLUTION ALGORITHM 
===========
SOLUTION ALGORITHM,
    CTF;                     !- SolutionAlgo
!-   ===========  ALL OBJECTS IN CLASS: SHADOWING 
CALCULATIONS ===========
SHADOWING CALCULATIONS,
    20;                      !- Period_for_calculations
!-   ===========  ALL OBJECTS IN CLASS: AIRFLOW MODEL 
===========
Airflow Model,
    Simple;                  !- AirFlowModelValue
!-   ===========  ALL OBJECTS IN CLASS: ZONE VOLUME 
CAPACITANCE MULTIPLIER ===========
ZONE VOLUME CAPACITANCE MULTIPLIER,
    1;                       !- Capacitance Multiplier
!-   ===========  ALL OBJECTS IN CLASS: LOCATION ===========
Location,
    SEOUL,                   !- LocationName
    37.55,                   !- Latitude {deg}
    126.8,                   !- Longitude {deg}
    9,                       !- TimeZone {hr (decimal)}
    19;                      !- Elevation {m}
!-   ===========  ALL OBJECTS IN CLASS: DESIGNDAY ===========
DesignDay,
    LGOSQSummer,             !- DesignDayName
    30.2,                    !- Maximum Dry-Bulb Temperature 
{C}
    4,                       !- Daily Temperature Range {C}
    20.4,                    !- Wet-Bulb Temperature At 
MaxTemp {C}
    100000,                  !- Barometric Pressure {Pa}
    2,                       !- Wind Speed {m/s}
    0,                       !- Wind Direction {deg}
    1,                       !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    1,                       !- Day Of Month
    8,                       !- Month
    SummerDesignDay,         !- Day Type
    0;                       !- Daylight Saving Time 
Indicator
DesignDay,
    LGOSQWinter,             !- DesignDayName
    -12.1,                   !- Maximum Dry-Bulb Temperature 
{C}
    0,                       !- Daily Temperature Range {C}
    -12.1,                   !- Wet-Bulb Temperature At 
MaxTemp {C}
    101100,                  !- Barometric Pressure {Pa}
    6.5,                     !- Wind Speed {m/s}
    10,                      !- Wind Direction {deg}
    0,                       !- Sky Clearness
    0,                       !- Rain Indicator
    0,                       !- Snow Indicator
    1,                       !- Day Of Month
    2,                       !- Month
    WinterDesignDay,         !- Day Type
    0;                       !- Daylight Saving Time 
Indicator
!-   ===========  ALL OBJECTS IN CLASS: MATERIAL:REGULAR 
===========
MATERIAL:REGULAR,
    C11,                     !- Name
    MediumRough,             !- Roughness
     .01,                    !- Thickness {m}
    1.72,                    !- Conductivity {W/m-K}
    2242,                    !- Density {kg/m3}
    830,                     !- Specific Heat {J/kg-K}
    .9,                      !- Absorptance:Thermal
    .7,                      !- Absorptance:Solar
    .7;                      !- Absorptance:Visible
MATERIAL:REGULAR,
    adiabatic,               !- Name
    MediumRough,             !- Roughness
    .3,                      !- Thickness {m}
    .0001,                   !- Conductivity {W/m-K}
    2242,                    !- Density {kg/m3}
    830,                     !- Specific Heat {J/kg-K}
    .9,                      !- Absorptance:Thermal
    .7,                      !- Absorptance:Solar
    .7;                      !- Absorptance:Visible
!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION 
===========
CONSTRUCTION,
    con-wall,                !- Name
    C11;                     !- Outside Layer
CONSTRUCTION,
    con-ceiling,             !- Name
    C11;                     !- Outside Layer
CONSTRUCTION,
    con-floor,               !- Name
    adiabatic;               !- Outside Layer
!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
ZONE,
    Floor0:Space1,           !- Zone Name
    0,                       !- Relative North (to building) 
{deg}
    0,                       !- X Origin {m}
    0,                       !- Y Origin {m}
    0,                       !- Z Origin {m}
    1,                       !- Type
    1,                       !- Multiplier
    2.946,                   !- Ceiling Height {m}
    27.405165,               !- Volume {m3}
    Detailed;                !- Zone Inside Convection 
Algorithm
!-   ===========  ALL OBJECTS IN CLASS: SURFACEGEOMETRY 
===========
SurfaceGeometry,
    LLC,                     !- SurfaceStartingPosition
    CCW,                     !- VertexEntry
    Relative;                !- SurfaceGeometryKey
!-   ===========  ALL OBJECTS IN CLASS: SURFACE:HEATTRANSFER 
===========
Surface:HeatTransfer,
    Wall1,                   !- User Supplied Surface Name
    WALL,                    !- Surface Type
    con-wall,                !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    3.04,                    !- Vertex 1 X-coordinate {m}
    3.04,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    6.09,                    !- Vertex 2 X-coordinate {m}
    3.04,                    !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    6.09,                    !- Vertex 3 X-coordinate {m}
    3.04,                    !- Vertex 3 Y-coordinate {m}
    2.946,                   !- Vertex 3 Z-coordinate {m}
    3.04,                    !- Vertex 4 X-coordinate {m}
    3.04,                    !- Vertex 4 Y-coordinate {m}
    2.946;                   !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Wall2,                   !- User Supplied Surface Name
    WALL,                    !- Surface Type
    con-wall,                !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    6.09,                    !- Vertex 1 X-coordinate {m}
    3.04,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    6.09,                    !- Vertex 2 X-coordinate {m}
    6.09,                    !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    6.09,                    !- Vertex 3 X-coordinate {m}
    6.09,                    !- Vertex 3 Y-coordinate {m}
    2.946,                   !- Vertex 3 Z-coordinate {m}
    6.09,                    !- Vertex 4 X-coordinate {m}
    3.04,                    !- Vertex 4 Y-coordinate {m}
    2.946;                   !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Wall3,                   !- User Supplied Surface Name
    WALL,                    !- Surface Type
    con-wall,                !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    6.09,                    !- Vertex 1 X-coordinate {m}
    6.09,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    3.04,                    !- Vertex 2 X-coordinate {m}
    6.09,                    !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    3.04,                    !- Vertex 3 X-coordinate {m}
    6.09,                    !- Vertex 3 Y-coordinate {m}
    2.946,                   !- Vertex 3 Z-coordinate {m}
    6.09,                    !- Vertex 4 X-coordinate {m}
    6.09,                    !- Vertex 4 Y-coordinate {m}
    2.946;                   !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Wall4,                   !- User Supplied Surface Name
    WALL,                    !- Surface Type
    con-wall,                !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0.5,                     !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    3.04,                    !- Vertex 1 X-coordinate {m}
    6.09,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    3.04,                    !- Vertex 2 X-coordinate {m}
    3.04,                    !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    3.04,                    !- Vertex 3 X-coordinate {m}
    3.04,                    !- Vertex 3 Y-coordinate {m}
    2.946,                   !- Vertex 3 Z-coordinate {m}
    3.04,                    !- Vertex 4 X-coordinate {m}
    6.09,                    !- Vertex 4 Y-coordinate {m}
    2.946;                   !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Floor1,                  !- User Supplied Surface Name
    FLOOR,                   !- Surface Type
    con-floor,               !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    OtherZoneSurface,        !- OutsideFaceEnvironment
    Floor1,                  !- OutsideFaceEnvironment Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    3.04,                    !- Vertex 1 X-coordinate {m}
    3.04,                    !- Vertex 1 Y-coordinate {m}
    0,                       !- Vertex 1 Z-coordinate {m}
    3.04,                    !- Vertex 2 X-coordinate {m}
    6.09,                    !- Vertex 2 Y-coordinate {m}
    0,                       !- Vertex 2 Z-coordinate {m}
    6.09,                    !- Vertex 3 X-coordinate {m}
    6.09,                    !- Vertex 3 Y-coordinate {m}
    0,                       !- Vertex 3 Z-coordinate {m}
    6.09,                    !- Vertex 4 X-coordinate {m}
    3.04,                    !- Vertex 4 Y-coordinate {m}
    0;                       !- Vertex 4 Z-coordinate {m}
Surface:HeatTransfer,
    Ceiling1,                !- User Supplied Surface Name
    CEILING,                 !- Surface Type
    con-ceiling,             !- Construction Name of the 
Surface
    Floor0:Space1,           !- InsideFaceEnvironment
    ExteriorEnvironment,     !- OutsideFaceEnvironment
    ,                        !- OutsideFaceEnvironment Object
    SunExposed,              !- Sun Exposure
    WindExposed,             !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Surface Vertice 
Groups -- Number of (X,Y,Z) groups in this surface
    3.04,                    !- Vertex 1 X-coordinate {m}
    3.04,                    !- Vertex 1 Y-coordinate {m}
    2.946,                   !- Vertex 1 Z-coordinate {m}
    6.09,                    !- Vertex 2 X-coordinate {m}
    3.04,                    !- Vertex 2 Y-coordinate {m}
    2.946,                   !- Vertex 2 Z-coordinate {m}
    6.09,                    !- Vertex 3 X-coordinate {m}
    6.09,                    !- Vertex 3 Y-coordinate {m}
    2.946,                   !- Vertex 3 Z-coordinate {m}
    3.04,                    !- Vertex 4 X-coordinate {m}
    6.09,                    !- Vertex 4 Y-coordinate {m}
    2.946;                   !- Vertex 4 Z-coordinate {m}
!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPE 
===========
ScheduleType,
    Control Type,            !- ScheduleType Name
    0:4,                     !- range
    DISCRETE;                !- Numeric Type
ScheduleType,
    Temperature,             !- ScheduleType Name
    -60:200,                 !- range
    CONTINUOUS;              !- Numeric Type
!-   ===========  ALL OBJECTS IN CLASS: DAYSCHEDULE 
===========
DAYSCHEDULE,
    Summer Control Type Day Sch,
                             !- Name
    Control Type,            !- ScheduleType
    2,                       !- Hour 1
    2,                       !- Hour 2
    2,                       !- Hour 3
    2,                       !- Hour 4
    2,                       !- Hour 5
    2,                       !- Hour 6
    2,                       !- Hour 7
    2,                       !- Hour 8
    2,                       !- Hour 9
    2,                       !- Hour 10
    2,                       !- Hour 11
    2,                       !- Hour 12
    2,                       !- Hour 13
    2,                       !- Hour 14
    2,                       !- Hour 15
    2,                       !- Hour 16
    2,                       !- Hour 17
    2,                       !- Hour 18
    2,                       !- Hour 19
    2,                       !- Hour 20
    2,                       !- Hour 21
    2,                       !- Hour 22
    2,                       !- Hour 23
    2;                       !- Hour 24
DAYSCHEDULE,
    Winter Control Type Day Sch,
                             !- Name
    Control Type,            !- ScheduleType
    1,                       !- Hour 1
    1,                       !- Hour 2
    1,                       !- Hour 3
    1,                       !- Hour 4
    1,                       !- Hour 5
    1,                       !- Hour 6
    1,                       !- Hour 7
    1,                       !- Hour 8
    1,                       !- Hour 9
    1,                       !- Hour 10
    1,                       !- Hour 11
    1,                       !- Hour 12
    1,                       !- Hour 13
    1,                       !- Hour 14
    1,                       !- Hour 15
    1,                       !- Hour 16
    1,                       !- Hour 17
    1,                       !- Hour 18
    1,                       !- Hour 19
    1,                       !- Hour 20
    1,                       !- Hour 21
    1,                       !- Hour 22
    1,                       !- Hour 23
    1;                       !- Hour 24
DAYSCHEDULE,
    Summer Zone Temp Day Sch,!- Name
    Temperature,             !- ScheduleType
    24,                      !- Hour 1
    24,                      !- Hour 2
    24,                      !- Hour 3
    24,                      !- Hour 4
    24,                      !- Hour 5
    24,                      !- Hour 6
    24,                      !- Hour 7
    24,                      !- Hour 8
    24,                      !- Hour 9
    24,                      !- Hour 10
    24,                      !- Hour 11
    24,                      !- Hour 12
    24,                      !- Hour 13
    24,                      !- Hour 14
    24,                      !- Hour 15
    24,                      !- Hour 16
    24,                      !- Hour 17
    24,                      !- Hour 18
    24,                      !- Hour 19
    24,                      !- Hour 20
    24,                      !- Hour 21
    24,                      !- Hour 22
    24,                      !- Hour 23
    24;                      !- Hour 24
DAYSCHEDULE,
    Winter Zone Temp Day Sch,!- Name
    Temperature,             !- ScheduleType
    20,                      !- Hour 1
    20,                      !- Hour 2
    20,                      !- Hour 3
    20,                      !- Hour 4
    20,                      !- Hour 5
    20,                      !- Hour 6
    20,                      !- Hour 7
    20,                      !- Hour 8
    20,                      !- Hour 9
    20,                      !- Hour 10
    20,                      !- Hour 11
    20,                      !- Hour 12
    20,                      !- Hour 13
    20,                      !- Hour 14
    20,                      !- Hour 15
    20,                      !- Hour 16
    20,                      !- Hour 17
    20,                      !- Hour 18
    20,                      !- Hour 19
    20,                      !- Hour 20
    20,                      !- Hour 21
    20,                      !- Hour 22
    20,                      !- Hour 23
    20;                      !- Hour 24
!-   ===========  ALL OBJECTS IN CLASS: WEEKSCHEDULE 
===========
WEEKSCHEDULE,
    Summer Control Type Week Sch,
                             !- Name
    Summer Control Type Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Monday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Friday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Summer Control Type Day Sch,
                             !- SummerDesignDay DAYSCHEDULE 
Name
    Summer Control Type Day Sch,
                             !- WinterDesignDay DAYSCHEDULE 
Name
    Summer Control Type Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Summer Control Type Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Control Type Week Sch,
                             !- Name
    Winter Control Type Day Sch,
                             !- Sunday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Monday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Tuesday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Wednesday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Thursday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Friday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Saturday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- Holiday DAYSCHEDULE Name
    Winter Control Type Day Sch,
                             !- SummerDesignDay DAYSCHEDULE 
Name
    Winter Control Type Day Sch,
                             !- WinterDesignDay DAYSCHEDULE 
Name
    Winter Control Type Day Sch,
                             !- CustomDay1 DAYSCHEDULE Name
    Winter Control Type Day Sch;
                             !- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Summer Zone Temp Week Sch,
                             !- Name
    Summer Zone Temp Day Sch,!- Sunday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Monday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Tuesday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Wednesday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Thursday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Friday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Saturday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- Holiday DAYSCHEDULE Name
    Summer Zone Temp Day Sch,!- SummerDesignDay DAYSCHEDULE 
Name
    Summer Zone Temp Day Sch,!- WinterDesignDay DAYSCHEDULE 
Name
    Summer Zone Temp Day Sch,!- CustomDay1 DAYSCHEDULE Name
    Summer Zone Temp Day Sch;!- CustomDay2 DAYSCHEDULE Name
WEEKSCHEDULE,
    Winter Zone Temp Week Sch,
                             !- Name
    Winter Zone Temp Day Sch,!- Sunday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Monday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Tuesday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Wednesday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Thursday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Friday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Saturday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- Holiday DAYSCHEDULE Name
    Winter Zone Temp Day Sch,!- SummerDesignDay DAYSCHEDULE 
Name
    Winter Zone Temp Day Sch,!- WinterDesignDay DAYSCHEDULE 
Name
    Winter Zone Temp Day Sch,!- CustomDay1 DAYSCHEDULE Name
    Winter Zone Temp Day Sch;!- CustomDay2 DAYSCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE ===========
SCHEDULE,
    ZoneControlTypeSch,      !- Name
    Control Type,            !- ScheduleType
    Winter Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    5,                       !- End Month 1
    31,                      !- End Day 1
    Summer Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 2
    6,                       !- Start Month 2
    1,                       !- Start Day 2
    11,                      !- End Month 2
    30,                      !- End Day 2
    Winter Control Type Week Sch,
                             !- Name of WEEKSCHEDULE 3
    12,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    CoolingSetpointsSch,     !- Name
    Temperature,             !- ScheduleType
    Winter Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    5,                       !- End Month 1
    31,                      !- End Day 1
    Summer Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 2
    6,                       !- Start Month 2
    1,                       !- Start Day 2
    11,                      !- End Month 2
    30,                      !- End Day 2
    Winter Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 3
    12,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
SCHEDULE,
    HeatingSetpointsSch,     !- Name
    Temperature,             !- ScheduleType
    Winter Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 1
    1,                       !- Start Month 1
    1,                       !- Start Day 1
    5,                       !- End Month 1
    31,                      !- End Day 1
    Summer Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 2
    6,                       !- Start Month 2
    1,                       !- Start Day 2
    11,                      !- End Month 2
    30,                      !- End Day 2
    Winter Zone Temp Week Sch,
                             !- Name of WEEKSCHEDULE 3
    12,                      !- Start Month 3
    1,                       !- Start Day 3
    12,                      !- End Month 3
    31;                      !- End Day 3
!-   ===========  ALL OBJECTS IN CLASS: NODE LIST ===========
NODE LIST,
    Floor0:Space1List,       !- Node List Name
    Floor0:Space1_1,         !- Node_ID_1
    Floor0:Space1_2,         !- Node_ID_2
    Floor0:Space1_3;         !- Node_ID_3
NODE LIST,
    Floor0:Space1_Inlet,     !- Node List Name
    Floor0:Space1_1;         !- Node_ID_1
!-   ===========  ALL OBJECTS IN CLASS: CONTROLLED ZONE 
EQUIP CONFIGURATION ===========
CONTROLLED ZONE EQUIP CONFIGURATION,
    Floor0:Space1,           !- Zone Name
    Floor0:Space1_Equip,     !- List Name: Zone Equipment
    Floor0:Space1_Inlet,     !- List Name: Zone Inlet Nodes
    ,                        !- List Name: Zone Exhaust Nodes
    Floor0:Space1_2,         !- Zone Air Node Name
    Floor0:Space1_3;         !- Zone Return Air Node Name
!-   ===========  ALL OBJECTS IN CLASS: ZONE EQUIPMENT LIST 
===========
ZONE EQUIPMENT LIST,
    Floor0:Space1_Equip,     !- Name
    PURCHASED AIR,           !- KEY--Zone Equipment Type 1
    Floor0:Space1_Air,       !- Type Name 1
    1,                       !- Cooling Priority
    1;                       !- Heating Priority
!-   ===========  ALL OBJECTS IN CLASS: ZONE 
CONTROL:THERMOSTATIC ===========
ZONE CONTROL:THERMOSTATIC,
    Floor0:Space1_Thermostat,!- Thermostat Name
    Floor0:Space1,           !- Zone Name
    ZoneControlTypeSch,      !- Control Type SCHEDULE Name
    SINGLE COOLING SETPOINT, !- Control Type #1
    Cooling Setpoint with SB,!- Control Type Name #1
    SINGLE HEATING SETPOINT, !- Control Type #2
    Heating Setpoint with SB;!- Control Type Name #2
!-   ===========  ALL OBJECTS IN CLASS: SINGLE HEATING 
SETPOINT ===========
SINGLE HEATING SETPOINT,
    Heating Setpoint with SB,!- Name
    HeatingSetpointsSch;     !- Setpoint Temperature 
SCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: SINGLE COOLING 
SETPOINT ===========
SINGLE COOLING SETPOINT,
    Cooling Setpoint with SB,!- Name
    CoolingSetpointsSch;     !- Setpoint Temperature 
SCHEDULE Name
!-   ===========  ALL OBJECTS IN CLASS: PURCHASED AIR 
===========
PURCHASED AIR,
    Floor0:Space1_Air,       !- Purchased Air Name
    Floor0:Space1_1,         !- Zone Supply Air Node Name
    45,                      !- Heating Supply Air Temp {C}
    18,                      !- Cooling Supply Air Temp {C}
    .015,                    !- Heating Supply Air Humidity 
Ratio {kg-H20/kg-air}
    0.008;                   !- Cooling Supply Air Humidity 
Ratio {kg-H20/kg-air}
!-   ===========  ALL OBJECTS IN CLASS: REPORT VARIABLE 
===========
Report Variable,
    *,                       !- Key_Value
    Outdoor Dry Bulb,        !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Opaque Surface Inside Face Conduction,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Zone/Sys Sensible Heating Rate,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Zone/Sys Sensible Cooling Rate,
                             !- Variable_Name
    hourly;                  !- Reporting_Frequency
Report Variable,
    *,                       !- Key_Value
    Mean Air Temperature,    !- Variable_Name
    hourly;                  !- Reporting_Frequency
!-   ===========  ALL OBJECTS IN CLASS: REPORT ===========
Report,
    Variable Dictionary;     !- Type_of_Report
Report,
    Surfaces,                !- Type_of_Report
    DXF;                     !- Name_of_Report
Report,
    Construction;            !- Type_of_Report