Re: [EnergyPlus_Support] Re: Warning messages for running 3zvent.idf
On 27 Mar 2003, at 5:24, waspoorboy wrote:
> Thanks Mike.
> For the "orphan objects" warnings in the 3zvent run,
> does it indicate that CROSS MIXING and INFILTRATION
> are Not used in EnergyPlus whenever COMIS is involved ?
> [In other words, if "AIRFLOW MODEL, COMIS;" is stated
> in .idf, the CROSS MIXING and INFILTRATION module in
> EnergyPlus is turned off ?]
> The above also applies to VENTILATION and MIXING objects,
> since those four are "grouped", is it correct ?
Correct.
>
> If WCS is used but zone origin(s) were not (0,0,0),
> will EnergyPlus overide the zone origin(s) to (0,0,0)?
>
No. When WCS is used, the surface coordinates are all with respect
to the building origin, so non-zero zone origins have no impact on
surface geometry. Daylighting reference points are always relative
to the zone origin (even when WCS is used), so non-zero zone origins
are meaningful with WCS with detailed daylighting.
Mike
> Thanks again,
> Ming
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@g...> wrote:
> > The warnings are just informative and do not reflect any impact on
> > results.
> >
> > To get rid of "orphan objects" warnings, just delete the listed
> > objects. The objects are not used in this simulation and are not
> > needed.
> >
> > To get rid of the zone origin warning, set the zone origins to
> > (0,0,0). Changing to relative coordinates with the current zone
> > origins would alter the geometry of the building.
> >
> > Mike
>
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Get 128 Bit SSL Encryption!
> http://us.click.yahoo.com/xaxhjB/hdqFAA/xGHJAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Get 128 Bit SSL Encryption!
http://us.click.yahoo.com/xaxhjB/hdqFAA/VygGAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/