RE: [EnergyPlus_Support] Latitude parameter in PV module
Miguel: You are correct. It is not responding to the latitude. A
bug report has been posted (CR#5976).
Mike
On 5 Sep 2003, at 12:13, Miguel Angel Pascual wrote:
> Dear Mike,
>
> Thanks for your answer, but let me insist on the question a little
> bit. You have run the simulation with different weather files (I
> suppose with different data in Global Horizontal Radiation field) so
> it's clear that the results should be different. But if you take a
> weather file, and just change the latitude, you will get the same
> production that in the unchanged weather file simulation.
>
> I have tried it with annual simulation of the example "purchair.idf"
> with weather files: "USA_IL_Chicago-OHare_TMY2.epw" ,
> "USA_FL_Tampa_TMY2.epw" and "ESP_Barcelona_IWEC.epw". For each of this
> weather files I get the same production regardless the latitude value
> I write in the weather file. Of course, the PV-production in Chicago,
> Tampa and Barcelona are different.
>
> All these questions are derived of the fact that I am finding estrange
> optimum slope values for the weather in Barcelona. La latitude in
> Barcelona is around 42º and the maximum production is achieved with
> slope array values around 30º.
>
> Thanks for your patience.
>
>
>
>
>
>
> -----Mensaje original-----
> De: Michael J. Witte [mailto:mjwitte@xxxxxxxx]
> Enviado el: jueves, 04 de septiembre de 2003 18:25
> Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Asunto: RE: [EnergyPlus_Support] Latitude parameter in PV module
>
>
> It works OK here. I ran the same inputs with Chicaog and Phoenix
> weather data and got different results. The eplus.def file is a list
> of defaults and it does not reflect what is actually used for the
> TRNSYS run. To see the listing from the actual TRNSYS run, see the
> .trn output file in the same folder with the other EnergyPlus outputs
> for your run. Search for "latitude" and the trn file will list all of
> the parameters for the location that was used.
>
> If you find that the location data is changing in the trn file but you
> are still getting the same PV power output, check the inverter
> capacity. If it is too small, then it will choke the power output
> such that different locations might produce the same amount of power.
> But the number of hours of daylight would be different, so this might
> not be the issue.
>
> Mike
>
>
> On 4 Sep 2003, at 15:11, Miguel Angel Pascual wrote:
>
> > Dear Linda,
> >
> > I have already changed the latitude in the weather file (N2 field in
> > location object) and I still get the same PV electrical production.
> > I don't know if this is right: I have checked the Eplus.def file in
> > the "trnsyspv" directory and the LAT column in the radiation
> > processor is always 43.1. Do you know what's going on?
> >
> > Thanks in advance,
> >
> >
> >
> > -----Mensaje original-----
> > De: Linda Lawrie [mailto:linda@xxxxxxxxxx]
> > Enviado el: jueves, 04 de septiembre de 2003 14:20
> > Para: EnergyPlus_Support@xxxxxxxxxxxxxxx;
> > EnergyPlus_Support@yahoogroups. com
> > Asunto: Re: [EnergyPlus_Support] Latitude parameter in PV module
> >
> >
> > At 06:46 AM 9/4/2003, Miguel Angel Pascual wrote:
> >
> > >Hello,
> > >
> > >I am running a simulation with a PV object. After running a
> > >simulation, I have changed the latitude in the "Location" object,
> > >but I got the
> > same
> > >electrical production. Can anybody explain me where or how is the
> > >latitude defined in the PV object?
> >
> > The PV uses the same latitude as the Location and/or Weather File
> > used by simulation. In fact, you must use a weather file for the
> > current PV object and the weather file location information
> > overrides the Location object in the input file.
> >
> > So, you would need to change the weather file's latitude/longitude
> > in order to see a change.
> >
> > Cautiously.
> >
> >
> > Linda
> >
> > EnergyPlus WebSite: http://www.energyplus.gov
> > Owner: EnergyPlus_Support list
> > Member: EnergyPlus Development Team
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > Yahoo! Groups Sponsor
> >
> > ADVERTISEMENT
> >
> > <http://rd.yahoo.com/M=259538.3830715.5078802.1261774/D=egroupweb/S=
> > 17 05
> > 007389:HM/A=1712983/R=0/SIG=11u38u3s2/*http://hits.411web.com/cgi-bi
> > n/ hi t?page=1374-105951838331032> click here
> >
> > <http://us.adserver.yahoo.com/l?M=259538.3830715.5078802.1261774/D=e
> > gr ou pmail/S=:HM/A=1712983/rand=303372734>
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> > <http://docs.yahoo.com/info/terms/> .
> >
> >
> >
> >
> > [Non-text portions of this message have been removed]
> >
> >
> > ------------------------ Yahoo! Groups Sponsor
> > ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> > HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on
> > orders $50 or more to the US & Canada.
> > http://www.c1tracking.com/l.asp?cid=5511
> > http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> > --------------------------------------------------------------------
> > -~ ->
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to
> > http://docs.yahoo.com/info/terms/
> >
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@xxxxxxxx
>
>
>
> Yahoo! Groups Sponsor
>
> ADVERTISEMENT
>
> <http://rd.yahoo.com/M=259538.3830715.5078802.1261774/D=egroupweb/S=17
> 05
> 007389:HM/A=1712983/R=0/SIG=11u38u3s2/*http://hits.411web.com/cgi-bin/
> hi t?page=1374-105951838331032> click here
>
> <http://us.adserver.yahoo.com/l?M=259538.3830715.5078802.1261774/D=egr
> ou pmail/S=:HM/A=1712983/rand=527672836>
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> <http://docs.yahoo.com/info/terms/> .
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Buy Ink Cartridges or Refill Kits for Your
> HP, Epson, Canon or Lexmark Printer at Myinks.com. Free s/h on orders
> $50 or more to the US & Canada.
> http://www.c1tracking.com/l.asp?cid=5511
> http://us.click.yahoo.com/l.m7sD/LIdGAA/qnsNAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
>
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
>
>
>
>
>
>
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/
>
------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.
Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/