Re: [EnergyPlus_Support] Re: humidity control



Adding a humidistat will have no effect unless the appropriate HVAC 
equipment is present and activated.  

For dehumidification, the only equipment which currently responds to 
a humidistat is FURNACE:BLOWTHRU:HEATCOOL and 
UNITARYSYSTEM:BLOWTHRU:HEATCOOL with "high humidity control"=yes.  
See the FurnaceWithDXSystemRHcontrol.idf example file.  

For humidification, you also need a SET POINT MANAGER:SINGLE ZONE MIN 
HUM and a HUMIDIFIER:STEAM:ELECTRICAL object.  See the CVRhMinHum.idf 
example file.    

Mike

On 2 Oct 2003, at 15:25, HSIEH Chun-Ming wrote:

> Hello,
> I am trying on simulating the Zone Control:humidistat. But, ....
> Except the Zone/Sys Moisture Load Rate Predicted has some change,
> other outputs including Air Humidity Ratio and Zone Air Relative
> Humidity were exactly the same as the output of the file that doesnt
> have the Humidistat. Is there any example talking about the
> Humidistat? Thank you very much.
> 
> Chunming
> 
> donbshireyiii wrote:
> 
> > As stated previously in this forum, we are aware of this issue
> > and a model will be added later this year to account for latent
> > degradation of cycling coils.  It will be included in the next major
> > release of EnergyPlus (Spring 2004).
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Edward Lyon"
> > <eglyon@s...>
> > wrote:
> > > I am not sure that I would trust the results of a humidistat
> > > setting when running a DX cooling coil system.  The humidistat can
> > > probably
> > make
> > > the cooling coil operate, but the part load operation of the DX
> > coil
> > is
> > > currently not calculating a proper SHR correction for part load
> > > operation.  If you were to run a simple model and double the size
> > of
> > a
> > > DX cooling coil, you would see that there is more dehumidification
> > under
> > > part load conditions with the larger unit.  This is counter to
> > observed
> > > field performance of real DX equipment.  Your model probably over
> > > dehumidifies the space with part-load cooling and consequently
> > > never trips the humidistat operation when you most need it.
> > > Consequently, until the DX cooling model is modified, I would not
> > > trust either the calculated interior conditions or the energy
> > > consumption of an added humidistat control used with DX cooling.
> > >
> > > Ned Lyon
> > >
> > > Senior Staff Engineer
> > > Simpson Gumpertz & Heger Inc.
> > >
> > > 41 Seyon Street
> > > Building #1, Suite 500
> > > Waltham, MA  02453
> > >
> > > Phone:  781-907-9000
> > > Fax:  781-907-9009
> > >
> > >
> > > >>> shirey@a... 7/31/2003 8:50:49 AM >>>
> > > Yes the DX cooling coil responds to the humidistat.  Look at the
> > > documentation for the object UNITARYSYSTEM:BLOWTHRU:HEATCOOL or
> > > FURNACE:BLOWTHRU:HEATCOOL. Look at the fields related to "high
> > > humidity control".
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "zhaicq98"
> > <chaoqinz@a...>
> > > wrote:
> > > > Mike,
> > > >
> > > > Does the DX cooling coil respond to the humidistat? I compared
> > two
> > > > files, one with humidistat object, another one without
> > humidistat.
> > > > But the output of indoor air condition and energy consumption is
> > > > exactly the same.
> > > >
> > > > Thanks,
> > > > Chaoqin
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> > > > <mjwitte@g...> wrote:
> > > > > Yes, your understanding of the thermostat is correct.
> > > > >
> > > > > Also, the desiccant dehumidifier does not currently repond to
> > the
> > > > > humidistat.  It controls to a fixed leaving humidity ratio
> > > > specified
> > > > > in the desiccant object.
> > > > >
> > > > > Mike
> > > > >
> > > > >
> > >
> > >
> > > Yahoo! Groups SponsorADVERTISEMENT
> > >
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > appropriate
> > > folder in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > > Service.
> >
> >
> > Yahoo! Groups Sponsor
> > ADVERTISEMENT
> > <http://rd.yahoo.com/M=256694.3651271.4917408.1261774/D=egroupweb/S=
> > 1705007389:HM/A=1688501/R=0/SIG=11if1rb57/*http://webevents.yahoo.co
> > m/universal/seabiscuit/> 
> >
> >
> >
> > To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
> > appropriate folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> > Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service
> > <http://docs.yahoo.com/info/terms/>.
> 
> 
> -- 
> 
> ------------------------------------------------------
> HSIEH Chun-Ming, Doctor Student 
>    Hanaki & Aramaki Laboratory,
>    Department of Urban and Environmental Engineering,
>    Graduate School of Engineering,
>    The University of Tokyo
> Tel: +81-3-5841-6248 
> Fax: +81-3-5841-8530
> Mobile: +81-90-9385-8293
> ------------------------------------------------------
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> ------------------------ Yahoo! Groups Sponsor
> ---------------------~--> Upgrade to 128-Bit SSL Security!
> http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
> ---------------------------------------------------------------------~
> ->
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to
> http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Upgrade to 128-Bit SSL Security!
http://us.click.yahoo.com/p7cEmB/s7qGAA/yigFAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/