Re: [EnergyPlus_Support] DAYSCHEDULE:LIST and timesteps for analysis



When the time intervals in a schedule are different than the timestep, the 
values are interpolated to determine the appropriate value for the current 
timestep.  

The TIMESTEP IN HOUR object defines the length of the zone heat transfer time 
step.  This defines the maximum HVAC simulation time step, however, under 
certain conditions, the HVAC simulation may switch to a shorter time step.  
There is no user control over the HVAC timestep.

To report at the HVAC timestep, use the "Detailed" reporting frequency.

Mike


On 8 Dec 2003, at 19:35, mikemccarty79 wrote:

> Hi
> I was wondering if anyone has used a DAYSCHEDULE:LIST to specify an 
> event that occurs at a smaller timestep than is used by energy plus 
> analysis.  For example, if my timestep for analysis is every 15 
> minutes but I have a schedule that changes every minute, will I run 
> into problems.  I am looking at demand controlled ventilation and 
> would like to adjust the amount of outside airflow more often than 
> every 10 or 15 minutes.  Also, is there anyway to view events 
> happening in timesteps of less than 10 minutes?  
> 
> Thanks.
> 
> Mike McCarty
> Graduate Student, Mechanical Engineering
> Iowa State University
> 2043 Black Engineering
> Ames, IA 50010
> 515-294-3080
> mmccarty@xxxxxxxxxxx
> 
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx


------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/