No, that is not necessary, but it is another solution to the problem.  Until 
the pointer bug is fixed, there are two workarounds:

1.  Move all of the *-I and *-CORE zones (all zones that do not use 
DAYLIGHTING:DETAILED) to the end of the group of ZONE objects.

OR

2.  Leave the ZONE list as it is, and add DAYLIGHTING:DETAILED objects for the 
zones which do not currently use it.

I would recommend option 1 to save computation time.

Mike



On 16 Dec 2003, at 9:57, Wong, S L wrote:

> As you mentioned whether I should also add the zones of *-I and *-CORE into the
> DAYLIGHTING:DETAILED or ILLUMINANCE:MAP?
> 
> lee
> 
> At 01:57 PM 12/15/2003 -0600, you wrote:
> >This run ultimately crashed with the same problem that your smaller file 
> >had.
> >The order for the ZONE objects and the DAYLIGHTING:DETAILED objects must 
> >be the
> >same to avoid the pointer bug in the illuminance map module.  If I understand
> >your structure correctly, then all of the ZONE objects for the *-I and *CORE
> >zones must come after all of the other zones.
> >
> >Mike
> >
> >
> >On 12 Dec 2003, at 15:30, Michael J. Witte wrote:
> >
> > > Lee:
> > >
> > > When I first ran this on my machine it crashed due to "insufficient virtual
> > > memory".  Please run this file in ep-launch with "View-->Pause During
> > > Simulation" selected and confirm if you receive a similar error message.
> > >
> > > If so, this means that you need to increase the size of your virtual 
> > memory page
> > > file.  In Windows 2000, the procedure is as follow:
> > >
> > > Go to the control panel (Start --> Settings --> Control Panel)
> > > Open the System control panel
> > > Select the Advanced tab
> > > Select Performance Options
> > > Under Virtual Memory select Change
> > >
> > > In this dialog, you can set the sizes for paging files on each hard 
> > drive.  Your
> > > file is now running on my machine.  With some other applications open, 
> > the Task
> > > Manager (right-click the toolbar and open task manager) says I'm using 
> > nearly
> > > 1.4 GB of memory.  The big jump in memory came when the message 
> > "Calculating
> > > Daylighting Factors" showed in the EnergyPlus window.  It's been at 
> > that point
> > > for over an hour now.  You'll need to set your total paging file 
> > maximum size
> > > plus physical RAM to be greater than 1.4 GB in order for this to run.
> > >
> > > Mike
> > >
> > >
> > >
> > >
> > > On 10 Dec 2003, at 15:04, Wong, S L wrote:
> > >
> > > > Mike,
> > > >
> > > > The problem has been fixed. After that I've simulated a 40-storey 
> > building.
> > > > Each floor consists of four parameter zones which are the North, 
> > East, South
> > > > and West, so total no. of zones with daylighting control are 160. I 
> > followed
> > > > your instructions to generate illuminance maps of these zones and the run
> > > > period is from 1/1 to 12/31 hourly. After simulation, the file was 
> > crashed
> > > > again. Is it any limitation of E+ in generating illuminance maps 
> > (i.e. nos of
> > > > zones, nos. of day, etc.)? How can I fix it again?
> > > >
> > > > Thanks
> > > >
> > > > lee
> > > >
> > > > At 11:51 AM 12/3/2003 -0600, you wrote:
> > > > >There is an error in the zone pointers used to grab the reference point
> > > > >coordinates which are included in the illuminance map output.  These
> > > > >reference point coordinates will only be correct if the ZONE object list
> > > > >is 
> > parallel to
> > > > >the DAYLIGHTING:DETAILED object list.  Note that these coordinates 
> > are only
> > > > >listed for reference and do not impact the values in the illuminance 
> > map.
> > > > >
> > > > >In your case, the bad pointers lead to an array subscript error.  To 
> > fix this
> > > > >problem, change the order of your ZONE objects to match the order of 
> > your
> > > > >DAYLIGHTING:DETAILED objects.  In your file, the first ZONE object 
> > should be
> > > > >GFSP-N, then GFSP-E, GFSP-S, GFSP-W which is what you have.  But 
> > then the
> > > > >next ZONE objects should be SP-N, SP-E, SP-S, SP-W, RFSP-N, RFSP-E, 
> > RFSP-S,
> > > > >RFSP-W.
> > > > >
> > > > >Mike
> > > > >
> > > > >
> > > > >On 3 Dec 2003, at 10:23, leeslwong wrote:
> > > > >
> > > > > > I've just uploaded a input file (new.idf) for daylighting simulation
> > > > > > for a 3-storey building. I add the "illuminance map" function into my
> > > > > > file. After running, it crashed. I wonder if anyone can tell me 
> > what the
> > > > > > problem is and how it can be fixed.
> > > > > >
> > > > > > Thanks
> > > > > >
> > > > > > lee
> > > > > >
> > > > > >
> > > > > >
> > > > > > To unsubscribe from this group, send an email to:
> > > > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > > >
> > > > > > The primary EnergyPlus web site is found at:
> > > > > > http://www.energyplus.gov
> > > > > >
> > > > > > The group web site is:
> > > > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > > >
> > > > > > Attachments are not allowed -- please post any files to the 
> > appropriate
> > > > > folder
> > > > > > in the Files are of the Support Web Site.
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > >
> > > > > > Your use of Yahoo! Groups is subject to 
> > http://docs.yahoo.com/info/terms/
> > > > > >
> > > > >
> > > > >
> > > > >
> > > > >========================================================
> > > > >Michael J. Witte, GARD Analytics, Inc.
> > > > >EnergyPlus Testing and Support
> > > > >EnergyPlus-Support@xxxxxxxx
> > > > >
> > > > >
> > > > >
> > > > >To unsubscribe from this group, send an email to:
> > > > >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > > >
> > > > >The primary EnergyPlus web site is found at:
> > > > >http://www.energyplus.gov
> > > > >
> > > > >The group web site is:
> > > > >http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > >
> > > > >Attachments are not allowed -- please post any files to the appropriate
> > > > >folder in the Files are of the Support Web Site.
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >
> > > > >Your use of Yahoo! Groups is subject to 
> > http://docs.yahoo.com/info/terms/
> > > >
> > > >
> > > >
> > > >
> > > > To unsubscribe from this group, send an email to:
> > > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > > >
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > >
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > >
> > > > Attachments are not allowed -- please post any files to the 
> > appropriate folder
> > > > in the Files are of the Support Web Site.
> > > >
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > Your use of Yahoo! Groups is subject to 
> > http://docs.yahoo.com/info/terms/
> > > >
> > >
> > >
> > >
> > > ========================================================
> > > Michael J. Witte, GARD Analytics, Inc.
> > > EnergyPlus Testing and Support
> > > EnergyPlus-Support@xxxxxxxx
> > >
> > >
> > >
> > > To unsubscribe from this group, send an email to:
> > > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the appropriate 
> > folder
> > > in the Files are of the Support Web Site.
> > >
> > >
> > >
> > >
> > >
> > >
> > > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> > >
> >
> >
> >
> >To unsubscribe from this group, send an email to:
> >EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the appropriate 
> >folder in the Files are of the Support Web Site.
> >
> >
> >
> >
> >
> >
> >Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
> 
> 
> 
> 
> To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files are of the Support Web Site.
> 
> 
> 
> 
> 
> 
> Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/ 
> 


To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files are of the Support Web Site.




 

------------------------ Yahoo! Groups Sponsor ---------------------~-->
Buy Ink Cartridges or Refill Kits for your HP, Epson, Canon or Lexmark
Printer at MyInks.com. Free s/h on orders $50 or more to the US & Canada.
http://www.c1tracking.com/l.asp?cid=5511
http://us.click.yahoo.com/mOAaAA/3exGAA/qnsNAA/dkFolB/TM
---------------------------------------------------------------------~->

Yahoo! Groups Links

To visit your group on the web, go to:
 http://groups.yahoo.com/group/EnergyPlus_Support/

To unsubscribe from this group, send an email to:
 EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

Your use of Yahoo! Groups is subject to:
 http://docs.yahoo.com/info/terms/