RE: [EnergyPlus_Support] How to set initial conditions in a simulation? (zone temperature, etc...)




The warmup simulation is the first day of the runperiod (or the designday) 
repeated until loads and temperatures stay within the tolerances specified in 
the BUILDING object.  In the eio output file, the number of warmup days is 
reported.

If you wish to force a certain condition on a zone, you could try altering the 
weather data for the first day of the run period and setting it to be a custom 
day type with special thermostat day schedules to force the building to a 
certain state.  

Mike

On 10 Mar 2005, at 17:52, Miguel Angel Pascual Buisan wrote:

> 
> Dear Pedro,
> 
> The Runperiod or design day simulation starts after the execution of a
> warmup simulation. During this warmup simulation all the initial conditions are
> determined. 
> 
> As far as I know, setting the initial conditions is much more than fixing
> the zone temperatures so it?s not possible to set then freely.
> 
> I hope it helps you.
> 
> Miguel Ángel Pascual Buisan
> Departamento de Ingeniería
> 
> MIYABI       espacios urbanos bioclimáticos
> Leyre 11bis, 1ºC 31002 Pamplona
> Tel: 948 20 36 44     Fax: 948 20 78 60
> Email: mapascual@xxxxxxxxx
> 
> 
> -----Mensaje original-----
> De: Pedro Rodrigo [mailto:pedromanuelrc@xxxxxxxx] 
> Enviado el: jueves, 10 de marzo de 2005 16:41
> Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Asunto: [EnergyPlus_Support] How to set initial conditions in a simulation?
> (zone temperature, etc...)
> 
> 
> Hello everybody!!
> I work in a team of researchers in the University of
> Jaen,Spain. We´re trying to build control strategies
> for energy efficiency in buildings, using EnergyPlus.
> We don´t know how to set initial conditions in a
> simulation (zone temperature). We know how to select a
> period of the year but not the zone´s thermodinamical
> state.
> Do you know something about the matter? 
> Thank you, friends.
> Regards,
> Pedro
> 
> 
> 
> ______________________________________________ 
> Renovamos el Correo Yahoo!: ¡250 MB GRATIS! 
> Nuevos servicios, más seguridad 
> http://correo.yahoo.es
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/