There is a bug in version 1.2.2 which is causing this.  This has been fixed for 
the next release.  We are looking for a workaround to get this running in 
1.2.2.030.

Mike


On 5 Jun 2005, at 13:44, ingdallolio wrote:

> I'm uploading my file, it runs with v 1.2.1 when I ran it with 1.2.2
> I get the error message below although I transitioned the file.
> Any help would be more than apreciated.
> Andrea.
> 
> > > ** Severe  ** Inlet parameters for plant demand side splitter are
> > not
> > > physically possible **
> > > ** Problem in input for plant demand side HOT WATER LOOP **
> > > ** The maximum flow out of the splitter is less than the minimum
> > inlet
> > > flow **
> > > ** Flow rate inputs for the loop do not match flow requirements of
> > the
> > > various branches/components **
> > > ** Check your flow rates and make sure that flow balances between
> > the
> > > splitter inlet and outlets    
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e... wrote:
> > 
> > The problem may be still in your input files.   Version 1.2.1 just
> > didn't give you a warning.  We've added more warnings
> > and notices of potential problems in V 1.2.2.
> > 
> > 
> > 
> >                                        
> 
> >                       "ingdallolio"                                 
> 
> >                       <ing.dallolio@l...      To: 
> EnergyPlus_Support@xxxxxxxxxxxxxxx               
> >                       >                            
> cc:                                        
> >                       Sent by:                     Subject:  
> [EnergyPlus_Support] Re: Downloading       
> >                       EnergyPlus_Support@yaho         Version 
> 1.2.1                                     
> >                       
> ogroups.com                                        
> 
> >                                        
> 
> >                                        
> 
> >                       06/04/2005 09:26 
> AM                                        
> >                       Please respond 
> to                                        
> >                       
> EnergyPlus_Support                                        
> 
> >                                        
> 
> >                                        
> 
> >                                        
> 
> > 
> > 
> > 
> > Drury,
> > Do you mean that the problem is in our input files and they have to
> > be corrected in order to run with v.1.2.2 or you mean there is a
> > problem with v 1.2.2 ?
> > Thanks.
> > Andrea.
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Drury.Crawley@e... wrote:
> > >
> > > You should uninstall v 1.2.2 and reinstall 1.2.1.
> > > Contact me directly if you didn't keep a copy
> > > of 1.2.1 and we'll arrange a place for you to
> > > download.
> > >
> > > But it sounds as if the problems were still in
> > > 1.2.1 just not noted by E+.
> > >
> > >
> > >
> > >
> > 
> > >                       "colotupper"
> > 
> > >                       <tupper@c...>        To:
> > EnergyPlus_Support@xxxxxxxxxxxxxxx
> > >                       Sent by:
> > cc:
> > >                       EnergyPlus_Support@yaho      Subject:
> > [EnergyPlus_Support] Downloading Version
> > >                       ogroups.com
> > 1.2.1
> > >
> > 
> > >
> > 
> > >                       05/27/2005 11:56
> > AM
> > >                       Please respond
> > to
> > >
> > EnergyPlus_Support
> > 
> > >
> > 
> > >
> > 
> > >
> > 
> > >
> > >
> > >
> > > Does anyonoe know if there's a way to reinstall Version 1.2.1 
> after
> > > installing V1.2.2?
> > >
> > > None of my files work with the new version, and I need to run them
> > to
> > > produce a report that's due at the end of next week.
> > >
> > > I ran the transition program and manually fixed many errors, but 
> any
> > > files with Hot Water Loops generate the following error.
> > >
> > > ** Severe  ** Inlet parameters for plant demand side splitter are
> > not
> > > physically possible **
> > > ** Problem in input for plant demand side HOT WATER LOOP **
> > > ** The maximum flow out of the splitter is less than the minimum
> > inlet
> > > flow **
> > > ** Flow rate inputs for the loop do not match flow requirements of
> > the
> > > various branches/components **
> > > ** Check your flow rates and make sure that flow balances between
> > the
> > > splitter inlet and outlets
> > >
> > > None of my flow rates are being autosize, and I have made sure all
> > the
> > > inlet flows equal the outlet flows.  Has anyone else had this
> > problem
> > > with the new version?  I read some other messages about this same
> > > error, but the folks were able to fix it using V1.2.1 - my files 
> all
> > > ran fine with the older version, so if anyone knows where to get 
> the
> > > old version, I would appreciate it!
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > appropriate
> > > folder in the Files area of the Support Web Site.
> > >
> > >
> > >
> > > Yahoo! Groups Links
> > >       To visit your group on the web, go to:
> > >       http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > >       To unsubscribe from this group, send an email to:
> > >       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >
> > >       Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service.
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
> appropriate
> > folder in the Files area of the Support Web Site.
> > 
> > 
> > 
> > Yahoo! Groups Links
> >       To visit your group on the web, go to:
> >       http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> >       To unsubscribe from this group, send an email to:
> >       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > 
> >       Your use of Yahoo! Groups is subject to the Yahoo! Terms of 
> Service.
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/