1.  You are correct, Purchased Air does not control indoor humidity.  There is 
no humidity control equivalent to Purchased Air.

2.  The Window AC also cannot control humidity.

3.  DX systems which can control humidity are FURNACE:BLOWTHRU:HEATCOOL, 
UNITARYSYSTEM:BLOWTHRU:HEATCOOL, and DXSystem:AirLoop.  See example files 
FurnaceWithDXSystemRHcontrol.idf and SmOffPSZ-MultiModeDX.idf.  Note that 
SmOffPSZ-MultiModeDX.idf uses the COIL:DX:MultiMode:CoolingEmpirical.  
DXSystem:AirLoop can also do humidity control using the single-stage  
COIL:DX:CoolingBypassFactorEmpirical coil type.

Mike


On 4 Nov 2005, at 20:37, wah wrote:

> Hello.
> 
> I would like to model an air conditioner that controls 
> indoor air temperature and humidity ratio.
> Currently I am using PurchasedAir for Heating and Cooling.
> I desire the function of SetPointManager:SingleZoneMaxHum.
> 
> My question:
> 1. From my understanding, Purchased Air cannot control the 
>    Humidity Ratio to a user setpoint.
>    Is there any equipment that can just control the Humidity to the SetPoint?
> 
> 2. If not, I suppose an option would be Window AC?
>    There is a Window AC Latent Zone Cooling Energy Output,
>    is that the energy needed to dehumidify the room air according 
>    to the user Humidity Setpoint?
>    How could I link the SetPointManager:SingleZoneMaxHum to Window AC?
> 
> 3. Or is there other better way to do it?
> 
> Please advice and thank you!
> 
> PuiWah
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
Fair play? Video games influencing politics. Click and talk back!
http://us.click.yahoo.com/T8sf5C/tzNLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/