Re: [EnergyPlus_Support] about the chiller coefficient



These coefficients change depending on the specific chiller specifications.  
The most accurate way to get these coefficients is to get performance data 
(capacity and power consumption) for a set of data points covering a range of 
entering chilled water and condenser water temperatures and build a spreadsheet 
to curve-fit the coefficients.  If you just want representative data, 
DataSets\PerfData.idf contains some curve data for CHILLER:ELECTRIC:EIR for 
centrifugal and reciprocating chillers.  What is the "chiller stylebook"?

Mike


On 24 Aug 2006 at 9:08, dreamerfish8146 wrote:

> Dear all:
>    I have some problems on the plant equipment field.I have to give 
> many coefficients for the chiller when I use the Chiller:Electric. For 
> example, there are three coefficients for the capacity ratio curve.I 
> wondered how can I get these coefficients. Are they supplied by the 
> chiller stylebook?But I can not find them on the book.Are these 
> coefficients fixed for all different chillers? Thanks a lot!
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the
> "search" button.
>  
> Yahoo! Groups Links
> 
> 
> 
>  
> 
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.idf and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/