Re: [EnergyPlus_Support] Re: modelling night sky cooling



This thread has taken some turns and I'm not sure if everything has been 
answered - sorry if I'm duplicating.

1.  Answered elsewhere by Linda.

2. EnergyPlus only models the case of a heat exchanger embedded in the pond..  
Increasing the quantity of tubing and decreasing its thermal resistance (thin 
with high conductivity) should approach the direct fluid case.

3.1 Yes.  I assume you've looked at the pond example file?  
PondHeatExchanger.idf

3.2 Yes.

4. Not exactly.  The pond will not be simulated if it is not connected to a 
plant or condenser loop, so it must be part of a larger model.  I have not 
tried this, but I think you could start with the example file 
PlantLoadProfile.idf, add the pond, schedule all of the pumps off, and see the 
pond temperatures.

Mike


On 18 Feb 2008 at 6:28, bish.dj61 wrote:

> Hi All
> I have been poring over the Ground Heat Exchanger:Pond engineering 
> ref, input/output ref, and example providedy with E+, so far with 
> fairly little progress. All I want to do is compare the use of a 
> cooling tower supplying a heat exchanger with the use of a pond:I 
> have some questions: 
> 
> 1) Does the sky temp come with a standard weather file?
> 2) Does the pond heat exchanger have to act as a heat exchanger, or 
> can water be pumped out of it into a heat exchanger, then returned?
> 3) I'm trying to get my head around how everything fits together, 
> so : 
>    3.1) Do all the components of the system exist on a "Plant Loop"
>    3.2) Are they all connected through "branches" and "nodes"?
> 4) Is it possible to run it standalone to simplify it so that I can 
> just see what temperature the pond reaches overnight?
> 
> cheers
> Danny
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "mapascualb" 
> <mapascual@...> wrote:
> >
> > I have got a few questions about night sky cooling:
> > 
> > - Can we use GROUND HEAT EXCHANGER:Surface ?  Does this model use 
> sky 
> > temperature? We don't want to use the "pond" model because our 
> > surface will be dry.
> > 
> > - How is determined the sky temperature in the design day? Can we 
> > control it? I could't find it in the engineering manual.
> > 
> > - Are the sky tempeatures included in the weather file realistic? I 
> > was expecting night summer sky temperatures below -20ºC for clear 
> days
> > and the temperatures I have seen are above 0ºC. What is the usual 
> > range of sky temperatures for a summer night in mid lattitud place? 
> > (I am sorry for the off-topic).
> > 
> > 
> > Thanks.
> > 
> > 
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> > <mjwitte@> wrote:
> > >
> > > GROUND HEAT EXCHANGER:POND may be used to model this effect.  See 
> > descriptions 
> > > in Input Output Reference and Engineering Reference, and example 
> > file 
> > > PondHeatExchanger.idf.
> > > 
> > > Mike
> > > 
> > > 
> > > On 8 Feb 2008 at 7:20, bish.dj61 wrote:
> > > 
> > > > hi All
> > > > Has anyone ever done, or have any idea on how to do night sky 
> > cooling 
> > > > modelling using the radiant temperature of the night sky to 
> cool 
> > water?
> > > > Any instruction or help would be greatly appreciated.
> > > > cheers
> > > > Danny
> > > > 
> > > > 
> > > > 
> > > > The primary EnergyPlus web site is found at:
> > > > http://www.energyplus.gov
> > > > 
> > > > The group web site is:
> > > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > > 
> > > > Attachments are not allowed -- please post any files to the 
> > appropriate folder
> > > > in the Files area of the Support Web Site.
> > > > 
> > > > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
> > under the
> > > > Documentation link and press the "search" button.
> > > > 
> > > > Yahoo! Groups Links
> > > > 
> > > > 
> > > > 
> > > > 
> > > > 
> > > 
> > > 
> > > ========================================================
> > > Michael J. Witte, GARD Analytics, Inc.
> > > EnergyPlus Testing and Support      
> > > EnergyPlus-Support@
> > >
> >
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> 
> Yahoo! Groups Links
> 
> 
> 
> 


========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/