[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Controller actuator error



If you use 18C, the cooling coil delta T goes to 0 because the system 
sizing object uses 18 as the Central cooling design supply air temperature.

Richard Raustad wrote:
>
> In the Zone Sizing object, I changed the zone cooling design supply air
> temperature from 18 to 12. The warnings are gone, and the cooling air
> flow is now 10.7 m3/s (and I didn't change the upper limit in the Load
> Range Based Operation objects). The higher the supply air temperature is
> in the zone sizing object, the higher the zone air flow rate. When I
> changed the zone sizing object to use a 14 degree zone cooling supply
> air temperature, the air flow rate jumped to 24 m3/s. If you set it at
> 18, there is basically a 0 degree delta T across the cooling coil and
> the air flow rate goes sky high.
>
> ZONE SIZING,
> ATRIUM, !- Name of a zone
> 12, !- Zone cooling design supply air temperature {C}
>
> brian.aldred@xxxxxxxxxxx <mailto:brian.aldred%40bentley.com> wrote:
> >
> > Thank you for your response, but whilst the loop demand error can be
> > removed in this way, in terms of the resultant airflow rates, we still
> > have a very high flow rates for the room (volume of ~830m³).
> >
> > Many of the components are auto sized, and looking at the eplusout.eio
> > file; we see the airflow rates auto size to just over 2e6 m³/s. I
> > don't know if this needs to be passed to a developer or not, but it
> > looks to me like the auto sizing is going awry somewhere.
> >
> > Any further suggestions would be appreciated.
> >
> > Brian
> >
> > ________________________________
> >
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <mailto:EnergyPlus_Support%40yahoogroups.com>] On Behalf Of Richard
> > Raustad
> > Sent: 18 April 2008 15:37
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > <mailto:EnergyPlus_Support%40yahoogroups.com>
> > Subject: Re: [EnergyPlus_Support] Controller actuator error
> >
> > Loop Demand=89853672305 W ? That's not a large room, it's a small 
> country.
> >
> > Check that this number is greater than the Load Range Upper Limit
> > specified in your file.
> >
> > If so, increase the load range upper limit and the equipment should
> > turn on:
> >
> > COOLING LOAD RANGE BASED OPERATION,
> > Central Chiller Only, !- Name
> > 0, !- Load Range Lower Limit 1 {W}
> > 900000, !- Load Range Upper Limit 1 {W}
> > Cooling Plant; !- Priority Control Equip List Name 1
> >
> > brian.aldred@xxxxxxxxxxx <mailto:brian.aldred%40bentley.com> 
> <mailto:brian.aldred%40bentley.com>
> > <mailto:brian.aldred%40bentley.com> wrote:
> > >
> > > I have an input file which describes a fairly large room served by a
> > > constant volume A/C system. When run with the two design days, I get
> > > errors for the controllers as follows:
> > >
> > > ** Warning ** No valid range found for Loop Demand=89853672305.89 in
> > > Load Range Based Operation Scheme=X1:CONTROL.
> > > ** ~~~ ** All equipment will be turned off. Other cases of this
> > > condition will not be reported.
> > > ** ~~~ ** During Warmup, Occurrence info=SUMMERDESIGNDAY, 07/15
> > > 05:00 - 05:15
> > > ** Warning ** No valid range found for Loop Demand=-3573128227.79 in
> > > Load Range Based Operation Scheme=Z1:CONTROL.
> > > ** ~~~ ** All equipment will be turned off. Other cases of this
> > > condition will not be reported.
> > > ** ~~~ ** During Warmup, Occurrence info=SUMMERDESIGNDAY, 07/15
> > > 08:00 - 08:15
> > > ** Severe ** FindRootSimpleController: Controller error for
> > > controller = A10:CONHEAT
> > > ** ~~~ ** Occurrence info=SUMMERDESIGNDAY, 07/15 07:00 - 07:15
> > > ** ~~~ ** Controller function is inconsistent with user
> > > specified controller action = Normal action
> > > ** ~~~ ** Actuator will be set to maximum action
> > > ** ~~~ ** Controller control type=Temperature
> > > ** ~~~ ** Controller temperature set point = 18.00 [C]
> > > ** ~~~ ** Controller sensed temperature = 16.39 [C]
> > > ** ~~~ ** Controller actuator mass flow rate set to 3106776.89
> > > [kg/s]
> > > ** ~~~ ** Controller actuator temperature = 16.25 [C]
> > > ** ~~~ ** Note: Chilled water coils should be reverse action
> > > and the entering chilled
> > > ** ~~~ ** water temperature (controller actuator
> > > temperature) should be below the setpoint temperature
> > > ** ~~~ ** Note: Hot water coils should be normal action and the
> > > entering hot
> > > ** ~~~ ** water temperature (controller actuator
> > > temperature) should be above the setpoint temperature
> > > ** Severe ** FindRootSimpleController: Controller error for
> > > controller = A10:CONCOOL
> > > ** ~~~ ** Occurrence info=SUMMERDESIGNDAY, 07/15 08:00 - 08:15
> > > ** ~~~ ** Controller function is inconsistent with user
> > > specified controller action = Reverse action
> > > ** ~~~ ** Actuator will be set to maximum action
> > > ** ~~~ ** Controller control type=Temperature
> > > ** ~~~ ** Controller temperature set point = 18.00 [C]
> > > ** ~~~ ** Controller sensed temperature = 21.81 [C]
> > > ** ~~~ ** Controller actuator mass flow rate set to 1104896.15
> > > [kg/s]
> > > ** ~~~ ** Controller actuator temperature = 25.25 [C]
> > > ** ~~~ ** Note: Chilled water coils should be reverse action
> > > and the entering chilled
> > > ** ~~~ ** water temperature (controller actuator
> > > temperature) should be below the setpoint temperature
> > > ** ~~~ ** Note: Hot water coils should be normal action and the
> > > entering hot
> > > ** ~~~ ** water temperature (controller actuator
> > > temperature) should be above the setpoint temperature
> > >
> > > I am struggling to determine the cause (and fix) of this error and 
> would
> > > like to know if you can give any insights?
> > >
> > > As far as I can see, we are specifying everything correctly, and if I
> > > replicate the same hvac system in another similarly sized room I 
> do not
> > > get the error. The file has been uploaded as in - controller actuator
> > > error.idf
> > >
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>> 
>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>>> 
>
> >
> > >
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>> 
>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>
> > 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP 
> <http://f1.grp.yahoofs.com/v1/MH8ISJvGNt3-8l2-iELLPINwGbpBnd1UPahc2YoQcP>>> 
>
> > >
> > > 
> N6jLN908jlXIXTDGkHxBJGY-Hx941z8oEuIe2cMRFAd5xUcXCp224/_Problem_Submittal
> > > s/in%20-%20controller%20actuator%20error.idf> in the Files, Problem
> > > Submittals section.
> > >
> > > Any help you can give would be much appreciated.
> > >
> > > Please contact us further if you require any additional information or
> > > assistance.
> > >
> > > Brian Aldred
> > > Software Development
> > > Tel: 0114 255 6680
> > > Fax: 0114 255 6638
> > >
> > > Hevacomp Ltd is a company registered in England and Wales with company
> > > number 1523216
> > > Registered office: Smithywood House, Smithywood Crescent, 
> Sheffield, S8
> > > 0NU
> > >
> > > P Help save paper - do you need to print this email?
> > >
> > > [Non-text portions of this message have been removed]
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu 
> <http://www.fsec.ucf.edu>
> > <http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>> 
> <http://www.fsec.ucf.edu/ <http://www.fsec.ucf.edu/>
> > <http://www.fsec.ucf.edu/ <http://www.fsec.ucf.edu/>>>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> > [Non-text portions of this message have been removed]
> >
> >
>
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/