[EnergyPlus_Support] Re: Schedule Output in CSV



Thank you for your help, I really appreciate it !

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> You can usually report the schedule value based on how the schedule is used.
> 
> For example, if the schedule is used to place a set point at a node, use 
> this in your input file:
> 
>   Output:Variable,
>     *,                       !- Key Value
>     System Node Setpoint Temp,        !- Variable Name
>     hourly;                  !- Reporting Frequency
> 
> If the schedule is used in the thermostat object:
> 
> **  Output:Variable,
>     *,                       !- Key Value
>     Zone/Sys Thermostat Heating Setpoint,        !- Variable Name
>     hourly;                  !- Reporting Frequency
> 
>   Output:Variable,
>     *,                       !- Key Value
>     Zone/Sys Thermostat Cooling Setpoint,        !- Variable Name
>     hourly;                  !- Reporting Frequency
> 
> Check the rdd file to see what report variables are available for your 
> simulation.
> 
> le_carambar wrote:
> >
> >
> > Dear E+ users,
> >
> > The object output:schedules write schedule values in .eio files.
> > I would like make appear the value of schedules in csv file.
> >
> > Somebody have an idea ?
> >
> > Thanks a lot,
> >
> > Camille T.
> >
> > 
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/