Most of the chillers have a sizing factor input which can be used to adjust the capacity. You would use 0.33 for three chillers.
Chiller:Electric:EIR,
N15, \field Sizing Factor
\note Multiplies the autosized capacity and flow rates
\type real
\minimum> 0.0
\default 1.0
On 7/25/2011 6:56 AM, Jim Dirkes wrote:Dear Vinay,
One of the idiosyncrasies of autosizing in E+ is that it sizes EACH chiller for the TOTAL load. You may not have noticed that the 2nd chiller never operated, but I suspect that was the case.
You?ll have to size them manually for the capacity you desire. Use the capacity of ONE chiller as the total capacity required for your building.
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___