Wigs! Karen, which PlantLoop Output Variable name EXACTLY are you refering to? I'm busy with a very high profile, highly political Summer Design Day simulation at the minute, and I can't be less than 100% sure. I am looking specifically when and how much my peak Load for the plant is...we're talking in the range if Mega Joules so small mistakes = lots of money.
> On Mon, Aug 8, 2011 at 9:10 AM, Karen Walkerman <kwalkerman@...>wrote:
>
> > **
> >
> >
> > I have seen the same thing happen when the terminal unit is a 4-pipe fan
> > coil. I'm not sure if it happens with other systems. I believe it is the
> > subject of a bug-fix for the next round of Energy+.
> >
> > I have also found that the hourly results reporting for loop loads is a
> > little misleading. The hourly loop loads seem to be based on the difference
> > between the loop setpoint temperature and the current temperature, and not
> > the actual heat transferred by the loop. If you want to know how much heat
> > your loop is transferring, I suggest calculating it based on the flowrate
> > and inlet and outlet temperatures.
> >
> > --
> > Karen
> >> > On Mon, Aug 8, 2011 at 11:35 AM, Qianmin Zhang <zqianmin@...> wrote:
> >
> >>
> >>
> >> Hello,
> >>
> >> I have heat demand in both chilled water loop and hot water loop. I'm not
> >> expecting the heat demand in chilled water loop. My hvac map .svg file has
> >> the correct connection. Any one know why there is heating demand in chilled
> >> water loop? Attached is the hvac map generated from energyplus. Thanks a
> >> lot,
> >>
> >> Regards,
> >> Qianmin
> >>
> >>
> >
> >
>