Re: [EnergyPlus_Support] Re: Controlling cooling coils





Hi Jean,
 
I send you all abject that you requested:
 
Coil:Cooling:Water
 
Name Air Loop Zemin AHU Cooling Coil
Availability Schedule Name 10019
Design Water Flow Rate autosize
Design Air Flow Rate autosize
Design Inlet Water Temperature autosize
Design Inlet Air Temperature autosize
Design Outlet Air Temperature autosize
Design Inlet Air Humidity Ratio autosize
Design Outlet Air Humidity Ratio autosize
Water Inlet Node Name Air Loop Zemin AHU Cooling Coil Water Inlet Node
Water Outlet Node Name Air Loop Zemin AHU Cooling Coil Water Outlet Node
Air Inlet Node Name Air Loop Zemin AHU  Supply Fan Air Outlet Node
Air Outlet Node Name Air Loop Zemin Supply Side Outlet 1
Type of Analysis SimpleAnalysis
Heat Exchanger Configuration CrossFlow
Condensate Collection Water Storage Tank Name 
Controller:WaterCoil
 
Name Air Loop Zemin AHU Cooling Coil Controller
Control Variable Temperature
Action Reverse
Actuator Variable Flow
Sensor Node Name Air Loop Zemin Supply Side Outlet 1
Actuator Node Name Air Loop Zemin AHU Cooling Coil Water Inlet Node
Controller Convergence Tolerance autosize
Maximum Actuated Flow autosize
Minimum Actuated Flow 0.000
SetpointManager:Scheduled
 
Name Air Loop/1 Setpoint Manager
Control Variable Temperature
Schedule Name 10027
Setpoint Node or NodeList Name Air Loop Zemin Supply Side Outlet 1
Schedule:Compact
 
Name 10027
Schedule Type Limits Name Any Number
Field 1 Through: 12/31
Field 2 For: AllDays
Field 3 Until: 24:00
Field 4 14 
 
Best regards
 
From: Jean marais <jeannieboef@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, July 9, 2012 12:01 PM
Subject: [EnergyPlus_Support] Re: Controlling cooling coils

 
Please post the setpoint managers objects from the idf that describe how your coils are controlled. Please also post the coil object, as the errors indicate that the action direction is wrong. The sequence of the coils is not your problem, but the setpoint managers may be incorrectly set up. If the heating coil sees very cold air and is told to heat to a certain point, it is self defeating. This setup is handled by the setpoint managers.

--- In mailto:EnergyPlus_Support%40yahoogroups.com, Ayzer Akguc <alpayakguc@...> wrote:
>
> Hi Jean,
> Ã? 
> Thanks for your attention.
> Ã? 
> Yes, the sequencing as predicted. What is the importance of the sequencing ? Does changing of the sequencing solve my problem ?
> Ã? 
> Best regards.
>
>
> ________________________________
> From: Jean marais <jeannieboef@...>
> To: mailto:EnergyPlus_Support%40yahoogroups.com
> Sent: Saturday, July 7, 2012 11:43 PM
> Subject: [EnergyPlus_Support] Re: Controlling cooling coils
>
>
>
> Ã? 
>
> Please post an extract of your idf showing the setpoint managers that you are using for your coils. I assume you have cooling coil then heating coil then fan?
> Also post the schedules used in your setpoint managers.
>





__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___