Please post the setpoint managers objects from the idf that describe how your coils are controlled. Please also post the coil object, as the errors indicate that the action direction is wrong. The sequence of the coils is not your problem, but the setpoint managers may be incorrectly set up. If the heating coil sees very cold air and is told to heat to a certain point, it is self defeating. This setup is handled by the setpoint managers.
--- In
mailto:EnergyPlus_Support%40yahoogroups.com, Ayzer Akguc <alpayakguc@...> wrote:
>
> Hi Jean,
> Ã?
> Thanks for your attention.
> Ã?
> Yes, the sequencing as predicted. What is the importance of the sequencing ? Does changing of the sequencing solve my problem ?
> Ã?
> Best regards.
>
>
> ________________________________
> From: Jean marais <jeannieboef@...>
> To:
mailto:EnergyPlus_Support%40yahoogroups.com
> Sent: Saturday, July 7, 2012 11:43 PM
> Subject: [EnergyPlus_Support] Re: Controlling cooling coils
>
>
>
> Ã?
>
> Please post an extract of your idf showing the setpoint managers that you are using for your coils. I assume you have cooling coil then heating coil then fan?
> Also post the schedules used in your setpoint managers.
>