SummerTypical and WinterTypical are not valid keywords
there.
You have to specify typical in the RunPeriod for sizing, if you want to
use those for the sizing calcs. (And still specify the schedules
for SummerDesignDay/WinterDesignDay)
At 10:06 PM 1/22/2013, Aber Alvi wrote:
Thanks Karen. I used 99.6%
heating design conditions for WinterDesignDay and 1% cooling design
conditions for SummerDesignDay from the weather file in the SizingPeriod
and also changed it in the schedules and it works, but I'm just curious
to know why it doesn't size using the typical conditions from the weather
file.
Aber
From: Karen Walkerman
<kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, January 22, 2013 5:55 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating
load zero for all zones
Hi Aber,
In "Zone Control Type Sched" you need to use SummerDesignDay
and WinterDesignDay instead of SummerTypical and WinterTypical.
--
Karen
On Mon, Jan 21, 2013 at 11:36 PM, Aber Alvi
<aberalvi@xxxxxxxxx>
wrote:
-
- Hi Karen,
- Yes, below is the control type schedule and I have given the single
heating and cooling set point schedule I used in my email below. These
schedules apply to all zones.
- Zone Control Type Sched, !- Name
- Control
Type,
!- Schedule Type Limits Name
- Through:
12/31, !- Field
1
- For: SummerTypical,
!- Field 2
- Until:
24:00,
!- Field 3
-
2,
!- Field 4
- For: WinterTypical,
!- Field 5
- Until:
24:00,
!- Field 6
-
1,
!- Field 7
- For:
AllOtherDays, !- Field 8
- Until:
24:00,
!- Field 9
-
0;
!- Field 10
- Thanks,
- Aber
- From: Karen Walkerman
<kwalkerman@xxxxxxxxx>
- To:
EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sent: Monday, January 21, 2013 9:02 PM
- Subject: Re: [EnergyPlus_Support] Calculated cooling and heating
load zero for all zones
-
- Do you have a ZoneControl:Thermostat object?
- On Jan 21, 2013 10:46 AM, "Aber Alvi"
<aberalvi@xxxxxxxxx>
wrote:
-
- Another thing I notice in the sensible heat gain summary of the
output report of the same file is that opaque surface conduction and
other heat addition is zero for zones with surfaces exposed to the
ambient. The exposed surfaces boundary condition type is outdoor and is
exposed to the sun and wind. Any idea why this could be
happening?
- Thanks,
- Aber
- From: Aber Alvi
<aberalvi@xxxxxxxxx>
- To:
"
EnergyPlus_Support@xxxxxxxxxxxxxxx"
<
EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Sent: Monday, January 14, 2013 11:23 AM
- Subject: [EnergyPlus_Support] Calculated cooling and heating load
zero for all zones
-
- Hi,
- I'm getting the following warning for all the zones while trying to
model a building located in climate zone 1.
- ** Warning ** Calculated design cooling load for zone=OS:THERMALZONE
7 is zero.
-
** ~~~ ** Check Sizing:Zone and
ZoneControl:Thermostat inputs.
- ** Warning ** Calculated design heating load for zone=OS:THERMALZONE
7 is zero.
- ** ~~~ ** Check Sizing:Zone and
ZoneControl:Thermostat inputs.
- I've used the following single heating and single cooling setpoint
schedule using SizingPeriod:WeatherFileConditionType.
- Schedule:Compact,
-
Htg-SetP-Sch,
!- Name
-
Temperature,
!- Schedule Type Limits Name
- Through:
12/31, !- Field
1
- For:
WinterTypical,
!- Field 2
- Until:
24:00,
!- Field 3
-
21;
!- Field 4
- For:
SummerTypical,
!- Field 5
- Until:
24:00,
!- Field 6
-
11;
!- Field 7
- For:
AllOtherDays,
!- Field 8
- Until:
24:00,
!- Field 9
-
21;
!- Field 10
- Schedule:Compact,
-
Clg-SetP-Sch,
!- Name
-
Temperature,
!- Schedule Type Limits Name
- Through:
12/31, !- Field
1
- For:
SummerTypical,
!- Field 2
- Until:
24:00,
!- Field 3
-
23;
!- Field 4
- For:
WinterTypical,
!- Field 5
- Until:
24:00,
!- Field 6
-
50;
!- Field 7
- For:
AllOtherDays,
!- Field 8
- Until:
24:00,
!- Field 9
-
23;
!- Field 10
- I have used ZoneInfiltration:DesignFlowRate for the infiltration of
1.024 l/s/m2 using flow/exteriorarea as the design flow rate calculation
method. I have also checked the internal gain inputs and they don't seem
to be too high or low. The lighting power is in line with ASHRAE 90.1
requirements, number of people is 0.04 person/m2 and equipment load is
2.7 W/m2.
- Any suggestions?