[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones





Thanks for the clarification Karen and Linda.


From: Linda Lawrie <linda@xxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Wednesday, January 23, 2013 6:38 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones

 
SummerTypical and WinterTypical are not valid keywords there.

You have to specify typical in the RunPeriod for sizing, if you want to use those for the sizing calcs.  (And still specify the schedules for SummerDesignDay/WinterDesignDay)

At 10:06 PM 1/22/2013, Aber Alvi wrote:


Thanks Karen. I used 99.6% heating design conditions for WinterDesignDay and 1% cooling design conditions for SummerDesignDay from the weather file in the SizingPeriod and also changed it in the schedules and it works, but I'm just curious to know why it doesn't size using the typical conditions from the weather file.

Aber


From: Karen Walkerman <kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Tuesday, January 22, 2013 5:55 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones

 
Hi Aber,

In "Zone Control Type Sched" you need to use SummerDesignDay and WinterDesignDay instead of SummerTypical and WinterTypical.

--
Karen

On Mon, Jan 21, 2013 at 11:36 PM, Aber Alvi <aberalvi@xxxxxxxxx> wrote:
 
Hi Karen,

Yes, below is the control type schedule and I have given the single heating and cooling set point schedule I used in my email below. These schedules apply to all zones.

Zone Control Type Sched, !- Name
    Control Type,            !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: SummerTypical,      !- Field 2
    Until: 24:00,            !- Field 3
    2,                       !- Field 4
    For: WinterTypical,      !- Field 5
    Until: 24:00,            !- Field 6
    1,                       !- Field 7
    For: AllOtherDays,       !- Field 8
    Until: 24:00,            !- Field 9
    0;                       !- Field 10

Thanks,

Aber

From: Karen Walkerman <kwalkerman@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, January 21, 2013 9:02 PM
Subject: Re: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones

 
Do you have a ZoneControl:Thermostat object?
On Jan 21, 2013 10:46 AM, "Aber Alvi" <aberalvi@xxxxxxxxx> wrote:
 
Another thing I notice in the sensible heat gain summary of the output report of the same file is that opaque surface conduction and other heat addition is zero for zones with surfaces exposed to the ambient. The exposed surfaces boundary condition type is outdoor and is exposed to the sun and wind. Any idea why this could be happening?

Thanks,

Aber

From: Aber Alvi <aberalvi@xxxxxxxxx>
To: " EnergyPlus_Support@xxxxxxxxxxxxxxx" < EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Monday, January 14, 2013 11:23 AM
Subject: [EnergyPlus_Support] Calculated cooling and heating load zero for all zones

 
Hi,

I'm getting the following warning for all the zones while trying to model a building located in climate zone 1.

** Warning ** Calculated design cooling load for zone=OS:THERMALZONE 7 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=OS:THERMALZONE 7 is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.

I've used the following single heating and single cooling setpoint schedule using SizingPeriod:WeatherFileConditionType.

Schedule:Compact,
    Htg-SetP-Sch,            !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: WinterTypical,            !- Field 2
    Until: 24:00,            !- Field 3
    21;                    !- Field 4
    For: SummerTypical,            !- Field 5
    Until: 24:00,            !- Field 6
    11;                    !- Field 7
    For: AllOtherDays,            !- Field 8
    Until: 24:00,            !- Field 9
    21;                    !- Field 10

Schedule:Compact,
    Clg-SetP-Sch,            !- Name
    Temperature,             !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: SummerTypical,            !- Field 2
    Until: 24:00,            !- Field 3
    23;                      !- Field 4
    For: WinterTypical,            !- Field 5
    Until: 24:00,            !- Field 6
    50;                    !- Field 7
    For: AllOtherDays,            !- Field 8
    Until: 24:00,            !- Field 9
    23;                    !- Field 10

I have used ZoneInfiltration:DesignFlowRate for the infiltration of 1.024 l/s/m2 using flow/exteriorarea as the design flow rate calculation method. I have also checked the internal gain inputs and they don't seem to be too high or low. The lighting power is in line with ASHRAE 90.1 requirements, number of people is 0.04 person/m2 and equipment load is 2.7 W/m2.


Any suggestions?


Thanks,

Aber













__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___