Yip. That's what I mean...I like to hear it from you because you have a gift for words and concisely summarizing facts. I think your memory of the % of the spectrum for longwave is possibly too large, however the point was not the % of spectrum, but the aggregate Joules that that spectrum band carries relative to the other ones bands (such as short-wave/visual). I also can't say anymore from memory, but it was (is) significantly more than the other (usefull) bands.
That's why I was refering to 'bad blinds'. A good blind would have the naked metal finish where as a bad blind would be coated with some kind of colour. As soon as that happens the metal surface (e=.35) would become a painted surface (e=.95) even if it is white paint. Notice when we talk about emmissiviy we usually refer to InfraRed (long-wave) emmissivity, although, as you know each frequency actually has it's own. This is again because we use IR as an indicator because it carries so much of the total solar energy.
As you point out, this is actually not a trivial question.
The reason we doubt that the blinds would be detrimental is because of personal experience. I grew up in an am South African...the old houses that I made my experience in often had heavy draps (never mind reflective blindes) and it was an effective control measure to keep rooms cool.
What I suspect here is that we need to try this in a new fangled highly insulated, light mass building with low-e glazing and see if it still works.
I'm only now rarely experiencing this kind of build (like when I go on holiday), and they really are quite different. The last one I was in had windows to ventilate and floor heating controlled on an air thermostat. I found it increduabilly hard to control the temperatures and ventilation if the spaces. I ended up having one window constantly on tilt and one open upstairs with the thermostat set to 15 degrees. Too much draft, but the best combination I could find. Next time I'll pay more attention to the blinds :-). Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
Jean,
Sorry for the delay in responding, mostly because I had to read
your post several times to understand what you were driving at,
and am still not exactly sure (I feel a bit like a defendant at a
trial wondering whether the witness was speaking for or against me
:-) ).
My memory is that long-wave radiation is around 40% of the solar
spectrum, but I could be wrong. How much of it gets into a zone
varies greatly depending on the optical properties of the glazing,
esp. those with selective low-E coatings.
I was following the proposition that zone air temperatures might
be increasing due to the blinds converting short-wave to long-wave
that stays in the zone, thus heating up the air.
Thanks for pointing out that even long-wave radiation doesn't all
stay in the zone in the case of a blind sitting right behind a
window,
although in your fourth line "long wave... hits window
(e=0.7)...", shouldn't that be 70% and not 30% "reflected back
towards blind" ?
Without doing a Gauss-Seidel solution (:-)), I would guess the net
amount of long-wave radiation remaining in the zone from your
scenario between 50-60% on the window side. It would be 100% for
the long-wave on the zone side of the blinds, but that radiation
would be coupled to the floor slab as much as direct solar
radiation.
So, the question for me would be whether 25-30% conversion to
long-wave radiation would more than counteract the 80% rejection
of
short-wave radiation due to the blinds?
Joe
On 10/9/2014 11:17 PM, ' jeannieboef@xxxxxxxxx'
jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
I like the way you are breaking this down and would
love to hear also how you consider the LONG wave radiation
(which to my understanding carries the bigger "chunk" of
the energy).
I was thinking roughly as follows:
Long wave hits glass (emmissivity 0.7) --> 30% gets
through
Long wave hits slat (emmissivity highly variable... a
"bad" blind may be cheaply painted and have the
emmissivity degraded from 0.3 to 0.95) --> 5% hit floor
and 95% is absorbed and reradiated equally in both
directions.
Long wave from blind towards window --> hits window
(e=0.7) --> 30% reflected back towards blind -->
loop continues until dissipated (I'm assuming a
gauss-seidel or similarely solved differential equation)
So now comparing to (in FullExterior mode) all the
entering radiation hits floor and the reflected (0.5%) is
area weightedly distributed to all zone surfaces, the
windows amongst these recieve a significant portion to
reradiate (question is if the energy is reproportioned
appropriately into short wave and long wave reradiating
from the floor).
One aspect which is not talked about is whether the
model accounts for the locally increase air temperatures
between blind and window and the heat transfer from this
air to the outdoors. The surface temps of both blinds and
glass pane may significantly change surface airflows
(convection heat exchange from air to surface).
Mit freundlichen
Grü�en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel. +49 30 6706662-23
What you say is true, but it's not the only effect
of window blinds. Of the solar radiation that's
intercepted by window blinds, most of it is
reflected back out of the window depending on its
reflectance, a small fraction (< 5%) is
transmitted, and the remainder absorbed and
reradiated as long-wave radiation. So, when I hear
that window blinds actually increase the indoor air
temperature, this would imply that the reradiated
long-wave is significantly greater than the
reflected short-wave, which would happen only if the
blinds are heavy and dark. However, all the blinds
I've seen, especially those used for solar control,
are either white or very light in color.
It's pretty well-known that external blinds are more
effective than internal blinds for reducing unwanted
solar gain. However, this is the first I've heard
that internal blinds are not just ineffective, but
counter-productive. In rereading the original post,
I noticed it said "Zone mean air temperature" and
"Surface inside face temperature" have both gone
up. I'm not particularly surprised at the latter,
because blinds tend to have higher absorptivity than
glazing (although I would caution not to ignore the
transmitted short-wave through the window in
comparing surface temperatures), but I am surprised
at the former. I don't want to speculate further on
this until I know more how the blinds are being
modeled, how the zone is being controlled, and how
the HVAC, if there is one, is being modeled.
The following link is for a paper done in 2004
studying the same issue in a similar building (80%
glazing on the facades) and comparable climate
(Canada). That study concluded that internal blinds
reduced cooling loads on a continuum depending on
their reflectance, with the best (90% reflectance)
approaching but still significantly less effective
than external blinds.
http://sbrn.solarbuildings.ca/c/sbn/file_db/Doc_File_e/Simulation%20design%20study%20for%20the%20facade%20renovation.pdf
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 10/8/2014 10:58 PM, Almofeez almofeez@xxxxxxxxx
[EnergyPlus_Support] wrote:
It may be
explained that, the blinds absorb short
wave solar heat and radiate long wave heat.
We know glass is opaque to short wave
radiant heat. Therefore heat is trapped
inside room.
â??â?«Ù?Ù?
جÙ?از اÙ?Ù? iPhone اÙ?خاص بÙ?â?¬
I can't point to a study, but the guys
at trnsys have told me that studies have
shown that internal blinds bring little to
no positive effect on room heat gain.
However, as we're on the topic of
blinds, could someone please draw up a
table showing which controls are effected
by which input parameters, e.g. Control
type glare - does it go the the "fixed
slat" position on trigger or does it
change possition between min/max slat
angles to maintain a setpoint?
There are a lot of control options...a
table would be a great addition to the
documentaion.
Jean
Hmmm,
interesting. Wouldn't the blinds
reflect a fair amount of the solar
back out through the window? Seems
counter-intuitive that deploying
blinds behind a window will increase
rather than decrease the mean air
temperature of the space. Have we
been wrong all these decades? I'd
still
like to know the thermal/optical
characteristics of the window and
the blinds. I suppose having a black
blind behind a window with very low
IR transmissivity might create
problems.
Joe
On 10/8/2014 4:45 PM, 'Edward G.
Lyon' eglyon@xxxxxxx
[EnergyPlus_Support] wrote:
The low mass blinds
will also absorb all the
solar and transfer it to the
interior air. Without
blinds, the solar hits a
more massive floor/walls
with much less immediate
transfer to the air. This
could give you higher
cooling peak demand.
Ned Lyon, P.E. (MA,
WV)
Staff Consultant
SIMPSON GUMPERTZ
& HEGER
781.907.9000 main
781.907.9350 direct
617.285.2162 mobile
781.907.9009 fax
www.sgh.com
I suspect there's
something wrong in the
modeling of the blinds.
The effect of night sky
radiation is not so
pronounced on a window,
because (1) half of what
it sees is ground, (2)
the other half is the
sky at low angles where
the sky temperatures are
much less depressed as
they are looking
straight up the sky.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 10/7/2014 11:00 PM, 'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx
[EnergyPlus_Support]
wrote:
If you have a
building with lots
of glass, don't
forget the radiant
exchange with the
night sky at -60 C.
The "radiant night
cooling" is possibly
being blocked by the
blinds, if the
blinds are there
during the night.
Mit freundlichen Grü�en- Sent from my
iPhone (excuse
the brevity)
Hello,
I've designed a
south facing
room with a
floor-
to-ceiling
window and
blinds covering
the whole
surface of the
window. I run
two simulations,
one with no
blinds on the
window and one
with blinds
covering the
window in order
to compare the
results. The
building's
location is in
Eastern
Europe. The run
period is from
July to August
(sunny and
hot period).
Both output
variables "Zone
mean air
temperature" and
"Surface inside
face
temperature",
have much higher
values when the
simulation is
run with the
blinds on the
window. How can
this be
possible? Can it
be explained in
a way or is
there something
wrong with the
data?
Thanks in
advance,
Anna V.
__._,_.___
Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|