Re: [EnergyPlus_Support] Re: Unmet Hours from Outdoor Air Units in EnergyPlus





Hi Jean,

1). My primary HVAC system is VariableRefrigerantFlow, as far as i know it doesn't require an airloop. It behaves like an unitary AC split which only circulates refrigerant, and use available indoor air to cool the zone. I used only Sizing:Zone and/or Sizing:Parameters to adjust its capacity. The "Sensible" and "Ventilation Requirement" options are in Sizing:System which I don't use. To provide fresh air for occupants, another secondary system, a single zone OAU (ZoneHVAC:OutdoorAirUnit) was added on each zone and worked alongside the primary VRF unit.

2). All of the unmet hours are in cooling due to the warm humid climate of Surabaya - Indonesia.

3). I didn't use any availibility manager, I used Schedule:Compact to set it on and off. Does this av manager would enable us to get more control over zones?

4). I didn't't use setpoint manager either, is it different from ThermostatSetpoint? is it necessary?

5). The priority had been set in ZoneHVAC:EquipmentConnection, with OutdoorAirUnit was in the 1st sequence and VRF TU was in the 2nd.

I have uploaded my example file in my previous reply for Julien, would you mind checking them also?
Thank you for your kind attention.

Regards,
Ade

__._,_.___

Posted by: ad3_prasetya@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___